    I was working on a Climate packaged chilled water unit today with 4 circuits that each had faults on them.
    On one of the circuits i traced the fault to the compressor motor protector module.
    I linked out the module whilst checking the pressures and the temp of the compressor and monitoring the amps.
    The compressor ran fine and the circuit seemed to be running ok.
    My first question is, can just the motor protection module be replaced? See the pic below ( the picture isnt great sorry)
    My next question is, on the wiring diagram that i was following i found each circuit had aTEV bypass solonoid valve, but what is the purpose of this TEV bypass?
    Marc
    3,853
    Re: Motor protector module
    Hi Marc,
    That looks like a copeland scroll lecky box. Yes you can replace just the module (int69 scy?) There are different models though, one just measure the thermistors and the other also monitors the phases for reverse rotation protection.
    Don't know about the solenoid though
    Cheers Jon
    Mar 2006
    Merate (LC) - Italy
    2,549
    The answer is yes for the first question. That's a INT69SC from Kriwan. Website http://www.kriwan.de or .at
    I guess that the bypass for a TEV may be useful for vacuuming the circuit on suction side.
    Mar 2006
    Lancashire
    1,859
    28
    Hi Marc,
    Cheers Jon
    Yes it is a Copeland scroll, like i said though i wasn't sure if it could be replaced so thanks for your helping me out.
    Marc
    Mar 2006
    Lancashire
    1,859
    28
    Quote Originally Posted by NoNickName View Post
    Why would you need to vacuum, only the suction side?
    Is it something to do with a pump down procedure?
    Marc
    Mar 2006
    Lancashire
    1,859
    28
    Anybody
    Marc
    Mar 2006
    Merate (LC) - Italy
    2,549
    I meant to vacuum the whole circuit with just one pipe on the suction side.
    70
    4,703
    47
    Hi Marc.
    Just a little further info on the INT69 Series controllers. Most of which you probaly know - but someone may benifit!
    As Monkey Spanners already points out there as a large range of these controllers available.
    (See link below).
    A quick reset facility is available by interupting the mains supply for 5 mins.
    This overides the lock out and inbuilt time delays.
    For further info refer to the data sheet provided.
    http://www.kriwan.com/en/Protection_...ilyID__127.htm
    This second data sheet refers to the 15 differant ptc probe temperature responce options available. (60c to 180c )
    As to the TRV bypass solenoid definatly strange!!!
    I have seen something similar to do with liquid injection / Oil cooling.
    As you say hopfully someone can shed some light on what it is for.
    Cheers Grizzly.
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Mar 2007
    394
    Hi Marc
    Would be interesting to see a picture of this and any other valve arrangements on this system.
    TRASH101's Avatar
    Mar 2007
    394
    Just another thought, is it a heat pump?
    Mar 2006
    Lancashire
    1,859
    28
    Quote Originally Posted by TRASH101 View Post
    No it isnt a heat pump, i see where you are going with that and that is what i thought first of all, it must be a heat pump. But it isn't
    Marc
    Mar 2006
    Lancashire
    1,859
    28
    I took some pictures today, not the best but i have three of them so here goes
    Marc
    Mar 2006
    Lancashire
    1,859
    28
    Also the LP switch factory setting is 3bar why so high?
    The TEV bypass solonoid valve control relay is linked into the LP swich just before it and this also has a setting of 3bar- see attatched picture
    Marc
    Mar 2008
    40
    32
    Hot-gass bypass is often used for multiple evaporators, or... whenever a very precise temperature is required. (+/- 0,2°C) The liquid solenoid is switched by a PID regulator, but whenever temperature reaches setpoint, the compressor would slowly reach vacuum. To avoid this, the suction pressure is kept at a certain higher point through the hotgass bypass.
    What kind of cabinet is this?
    Jan 2008
    derbyshire
    Smile Re: Motor protector module
    Does the bypass line go into a filter drier and then into 3 way solenoid valve arrangement? allowing pump down to occur keeping any refrigerant before the solenoid on the tev side to be held for the circuit when the Lp cuts back in, this stops the compressor from having a large short cycling time.
    Mar 2006
    Lancashire
    1,859
    28
    Quote Originally Posted by majo View Post
    Its a chilled water packaged unit. Hot-gas by pass is fed from the discharge line though, this looks like its on the liquid line.
    Marc
    Mar 2005
    Birmingham U.K.
    70
    54
    Hi Marc
    The bypass solenoid valve pipe, does it run to another TEV onto the evaporator ?
    To cover for the full duty for the compressor they may have to stage the operation of the TEVs
    At full load both TEVs in operation at below 50% TEV with soleniod shuts off
    regards Bobjob
    Mar 2006
    Lancashire
    1,859
    28
    Quote Originally Posted by bobjob View Post
    Hi Marc
    regards Bobjob
    Yes it does run to another TEV onto the evaporator, how does it work then because i've never come across this before.
    Marc
    Mar 2006
    Lancashire
    1,859
    28
    and why would the pressure switch be set at 3 bar? the same as the Lp switch?
    Marc
    Mar 2006
    Lancashire
    1,859
    28
    Also if it was as you say then why would the solonoid be called TEV bypass solonoid becase it isn't bypassing it?
    Marc
    Mar 2005
    Birmingham U.K.
    70
    54
    Hi Marc
    Many of those Climate chillers were built in the factory to a clients spec.
    They would normally use there Hitachi chillers for standard work but if the customer required such things as low noise operation or low water flows,low temperature operation they would modify a Hitachi chiller or build something from scratch.
    The 2 TEVs may by used with the unloading
    The setting of the pressure switch should be above the LP cut out to unload the cylinders and close off the refrigerant going to the one TEV
    from your information do you have 4 circuits or do you have 4 compressors ?
    If its 4 compressors with only 2 refrigerant circuits, this would be a standard Climate chiller the pressure switch would probably switch off the one TEV and one of the compressors.
    regards Bob
    Mar 2005
    Lanzarote
    372
    My dad used to work for Climate and I asked him about this. He gave the exact same answer as Bob. So, I would go with what Bob said.
  23. #23
    Feb 2008
    63
    Marc,
    the TEV bypass is for low ambient conditions. It is energized for the 1st 30 secs after compressor start up to prevent the suction pressure dropping too low to cut out on LP and preventing the evaporator temp from dropping too low, thus giving the head pressure time to rise to a satisfactorily suitable level and hence raise the suction pressure.
    Hope this helps.