    Hello
    I read somewhere that suction accumulators can be useful in plated heat exchanger systems since with these plates the liquid refrigerant tends to condesate when the compressor is off.
    Why liquid receiver tends to condensate when compressor is off? can anyone explain?
    thanks
    Feb 2007
    2,473
    Re: Suction accumulators
    What actually happens on some systems (without a solenoid valve in the liquid line and pump down to stop) is that the plate heat-exchanger used as evaporator fills up with liquid as it's the coldest part of the circuit. When the compressor then starts, it will try and compress liquid refrigerant...
    A suction accumulator will reduce the risk of liquid reaching the compressor (so would a proper pumpdown)
    Tjune54's Avatar
    Tjune54 Guest
    Cool Re: Suction accumulators
    To answer your second question; with out a soleniod valvle for pump down. The refrigerant will continue to migrate to the coldest prt of the system (cold plates).
    When the level lquid level in the receiver drops below the king valve intake the refrigerant starts to boil and absorb heat. Thus dropping the tank below dewpoint and condensating where liquid touches the sides.
    Apr 2008
    Germany
    56
    10
    Thanks a lot to both
    Oct 2003
    5,630
    What's King Valve?
    Jun 2005
    California
    394
    The shutoff service valve on the receiver outlet
    Aug 2005
    5,302
    Quote Originally Posted by Peter_1
    What's King Valve?
    Peter, the king valve is the valve on the receiver that controls the liquid flow to the system (like wambat said).
    I have never heard an explanation of how this valve came to be named this though?
  1. Copeland select 6
    By Copman in forum Tools and Calculators
    Last Post: 27-05-2010, 09:01 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Should suction accumulators be insulated?
    By superheated in forum Commercial
    Last Post: 16-02-2008, 07:12 PM
  4. Benji
    By benji in forum Trouble Shooting
    Last Post: 30-01-2008, 01:25 PM
  5. Suction Accumulators
    By rsiyer in forum Technical Speculations
    Last Post: 15-06-2007, 04:16 AM