Hi My AC guy just installed a Daikin FTXM71R2V1B. Unfortunately the indoor unit is located in a quite enclosed location and the indoor unit’s internal temperature sensor tends to overread. This means that, after a while the temperature sensor reaches 31c (heating mode), and the unit cycle through/ goes into cooling mode. We tried to fit an external temperature sensor or wired controller but Daikin said that it is not possible to fit with that model. However looking at the PCB diagram there seems to be an option to move the thermistor to another location, away from the hot flow so it does not overreads. Has anyone got experience with that specific model? Either moving the internal thermistor or taking the temperature input from a wired controller (BRC1E63 or equivalent)? Many Thanks