Hello Everyone,

Had a problem with an ice machine today and was hoping for some advice. It's a DC model DC90A (Italian) reported not making ice. Switched on and compressor kicked in, condenser fan motor cycles on and off. Noted water pump not kicking in, not getting 240v supply. Adjusted mechanical defrost timer and got water pump to work. I suspect the timer is faulty as not getting a 230 v supply to the defrost solenoid valve.

I have ordered a new timer and evap stat was struggling without a manual to hand so I'm hoping I have diagnosed it properly. Lp r404a seemed fined around 20 psi.

Regards
Pie man