People seem to be willing to share valuable knowledge on this site. Grateful for any I might receive. AC had not been used about a month and breaker tripped at some point.Reset breaker, pressed remote, red operation light flashed briefly and rapidly, then only green timer light flashed two times,pause,two times pause,....Wall unit(ASU30CLX) fan started blowing but did not get cool.Observed outside unit fan not working Removed cover from outside unit AOU30CLX and saw dried up gekko across main terminals. Removed gekko, checked incoming voltage, good,235V. From another discussion on this site about Fujitsu's I started some voltage checks and right off discovered no voltage going out of power supply at terminals W28 and W29. Have I found the problem? A bad power supply PCB? Thanks in advance for any and all comments