15-03-2005, 02:22 PM #1
Pump Down cycle with EPR
Hi,
I've been servicing a couple of 4' open display merchandisers - each individually served by a dedicated condensing unit.
The system employs an evaporator pressure regulator and cycles on pump down via liquid solenoid valve.
I am concerned about proper pump-down control setting. The EPR is set at a minimum 18degF evaporator temperature (R-22). At times, when the EPR modulates, the suction pressure back to the compressor can drop to 15 to 20 psi so the cut-out is needed to be set lower than such occurance.
On pump-down (cut-out set at 5 to 10 psi) and cycle off, the suction pressure will rise to the 18degF SST pressure plus the superheat setting of the expansion valve (approx. 45 psi). Some short-cycling is evident during off-cycle, and obtaining satisfactory shut-down of the condensing unit under the cool ambient conditions that now exist is somewhat tedious.
I slept on it last night, and considered perhaps more satisfactory results would be obtained with use of a suction stop solenoid valve, as opposed to the liquid line solenoid valve in conjunction with the application of the EPR.
Any thoughts or observations?
Similar Threads
-
liquid ammonia pump calvitation
By Kathleen in forum Trouble ShootingReplies: 23Last Post: 20-05-2011, 02:18 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
pump down for reverse cycle systems
By abbasi in forum FundamentalsReplies: 4Last Post: 21-04-2006, 06:03 AM -
New pump
By Peter_1 in forum Air ConditioningReplies: 1Last Post: 13-12-2003, 06:19 PM -
System Pump Down
By Brian_UK in forum Technical SpeculationsReplies: 16Last Post: 25-10-2001, 10:39 PM