    Mar 2006
    Greece
    Question oil dilution+high pressure and temp.
    Hi, I would appreciate any input on this observation I made.
    A scroll compressor that works with R-22 was vibrating during operation a bit more than normal. This caused the pipes to break. I noticed that the heat pump was operating on heat at 24-25 bar discharge pressure due to dirty, blocked air filters. My opinion is that that the oil in the faulty compressor was diluted due to working at high pressure and temperature for 18 months. This resulted in the eventual breakdown of the compressor which resulted in the vibration.
    Aug 2005
    5,302
    Re: oil dilution+high pressure and temp.
    I don't think I would call this a dilution problem. This occurs when the oil has liquid refrigerant in it. The oil viscosity is lowered when the refrigerant is mixed with the oil.
    In your example the oil viscosity was decreased by the high temperatures due to the air flow restriction. In addition to the lower oil viscosity issue the higher operating pressures would apply additional forces to the compressor bearings and other lubricated parts.
    Mar 2006
    Greece
    Thanks for your input Iceman. I meant the viscosity but my English was incorrect. Thanks for pointing it out.
    Oct 2003
    5,630
    I personally think that the chemical engineers make that the oil holds it lubrification capacities while working under different conditions.
    24 to 25 bar (348/362 psi) is high but is for the oil not such a big deal.
    Oil can decompose as soon discharge temperature reaches 140°C (284°F)
    Jun 2005
    S****horpe
    135
    24bar? Blimey. You could have had some air in there, raising the head pressure and making the compressor have to work very hard, hence the vibrations.
    It's a lovely day to pump some gas
  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Last Post: 13-04-2010, 08:58 PM
  2. GSHP discharge temp high
    By Lc_shi in forum Trouble Shooting
    Last Post: 20-01-2005, 08:37 AM
  3. Noobie question.Evaporator Pressure.
    By kfjoe in forum Fundamentals
    Last Post: 04-03-2003, 09:11 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Last Post: 16-07-2002, 02:10 PM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Last Post: 08-05-2002, 05:19 AM