11-10-2016, 09:07 PM #1
UNISAB RT Control
Hello!
Iīm looking for a manual for a UNISAB RT control for a SABROE PHE Chiller with two CMO-28 mounted. We get the A-1 alarm,however, no alarm light is on
Best regards
Thomas
Industrikyla AB Sweden
-
12-10-2016, 01:47 PM #2
Re: UNISAB RT Control
Hi, Thomas Cold
Maybe is not the best time to ask... but just for curiosity ... how you succeed to setup your PHE chiller without manual? ....
Anyhow ...if you go to UNISAB II R page with alarms and warnings you probably can see identification number .... the list is below ...
UNISAB II R alarm-warning ID numbers.pdf
If you need something more do not hesitate to ask
Hope this will be of some help.
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
16-10-2016, 09:25 AM #3
Re: UNISAB RT Control
Thankīs Josip!
Itīs a old chiller that dosenīt work propely! The chiller workīs a few hours than the AL-1 alarm comes and the chiller stop. The alarm will be completely at different times, so there is no logic in the problem.
We are going to help another ref.company that dosenīt work with this type of unit. They have a customer that need some help. So that why they called us! But the main problem is that we donīt have a service and installation manual for UNISAB RT Control, so if you have one that you can share us, i would be pleased.
-
16-10-2016, 09:50 AM #4
Re: UNISAB RT Control
Hi Thomas.
Welcome to the forum.
I like the fact that you have given some info about yourself (within your profile),
I have sent you some old info that I have.
It may not be complete and as I said is dated.
But it may Help?
Good luck GrizzlyDespite the High Cost of Living it still remains Popular!
-
16-10-2016, 10:20 AM #5
Re: UNISAB RT Control
Hi Thomas.
A1
Is a fault on feedback from the motor starter.
Which on newer unisabs generally means the run signal has timed out.
Hp switch dropped out? Auxillary contact from motor start panel not made ect.ect
A common mistake is when locked out on HP.
The HP switch is reset using the external button. But on the commonly used,dual Danfoss switches there is a internal rest switch.
Which if not reset the comp / system is still locked out on the above fault.
Good luck GrizzlyDespite the High Cost of Living it still remains Popular!