    problem with vfd interference



    I started a rack today. I have an e2 rx and bx and a Danfoss 5000 drive on my condenser.The problem is when I put the drive in inverter mode I loose my io boards. and the rx can't see the bx. I changed out the inverter to no avail. When the drive is in bypass all the boards come online. I called danfoss and was told to ground the 485 center com which i did. the filter on the drive is enabled. The one thing I do notice is when the ground from the condenser to the rack is disconnected the boards go on and off when I reconnect it just the bx goes off line. Any suggestions would be helpful. Everything is grounded well. I'm wondering if I'm getting any backfeeding any where.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: problem with vfd interference

    Are there any 'shielded' cables in the system which have been grounded at both ends? If yes then remove one end otherwise the shield acts as an aerial.

    Can you change the frequency that the inverter operates at? This can be a source of problems on some systems.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2007
    Location
    USA
    Age
    59
    Posts
    145
    Rep Power
    18

    Re: problem with vfd interference

    The shield is grounded and I removed it to no avail. I changed some parameters on inverter. No luck

  4. #4
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: problem with vfd interference

    Quote Originally Posted by Brian_UK View Post
    Are there any 'shielded' cables in the system which have been grounded at both ends? If yes then remove one end otherwise the shield acts as an aerial.

    Can you change the frequency that the inverter operates at? This can be a source of problems on some systems.
    By this I think he means the switching frequency, usually max setting 4.0 khz, try dropping to 3.5 or down to 3.0 - the drive may start to squeal more and the motors will quieten.

    Sounds like your backfeed is caused by bad shielding or poor cabling,
    is data (digital I/O, 0-10V signal, RS485 or Echelon cables) run parallel to mains cabling - especially cabling from the output of the drive? Big no no
    Are the power cables screened going to the condenders from the filters? not necessary but good practice
    Are these cables grounded at the VSD end on the grounding plate Danfoss supplies with a clamp setup around the braid? very necessary
    Are the low voltage/data cables screened and earthed at the mount supplied by Danfoss as well? all should be
    Is the filter earthed properly? should be
    Are the Echelon and/or RS485 cables' shield run to earth at the E2 end?
    Are you using echelon I/O cards or RS485? Coz if you have RS485 then it should be earthed in EACH E2 at one end of each I/O network and then the main echelon loop earthed at ONE end only - this means only one E2 either RX or BX. But if all cards echelon then one loop with one earthed end only.
    If echelon is the cable up to CPC spec? Is the cable up to any spec? coz poor unshielded cable = headaches
    Last edited by 750 Valve; 15-10-2007 at 02:58 PM.
    ...and she said "give it to me you big fridgie"

  5. #5
    Join Date
    Jan 2007
    Location
    USA
    Age
    59
    Posts
    145
    Rep Power
    18

    Re: problem with vfd interference

    Turns out that the cat 5 cable from the bx to the rx was run in pvc pipe next to the high voltage line of vfd. We ran in metal emt a different way and it worked fine.

  6. #6
    Join Date
    Nov 2007
    Location
    USA
    Posts
    9
    Rep Power
    0

    Re: problem with vfd interference

    This sounds like a wal-mart rack. We have been having a lot of installation problems with the VFD commisioning projects. Of course when your performing upgrades like these on 400 stores per year you are bound to hit a snag ever so often.

Similar Threads

  1. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  2. what's the problem
    By botrous in forum Air Conditioning
    Replies: 35
    Last Post: 22-06-2008, 02:54 AM
  3. Oil carry over Problem in Refrigeration Unit
    By imranmd in forum Industrial
    Replies: 1
    Last Post: 27-08-2007, 03:09 PM
  4. LG 10.5 kw cassette timer problem
    By Andy W in forum Air Conditioning
    Replies: 10
    Last Post: 25-06-2005, 07:09 PM
  5. RFI Interference from Fridge/Freezer
    By pathfinder in forum Trouble Shooting
    Replies: 6
    Last Post: 19-03-2005, 11:50 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •