    Smile condensing unit installation



    The compressor Rack is located at the second level of the building, the condensing unit is to be installed below the rack which is the ground floor.Is it advisable to install condensing unit to be installed below the compressor rack. Will it reduce system capacity considering it needs enough force for the liquid from the condenser to go up then down to the refrigerated cases?
    Any idea how to compute the losses or the bad side with this kind of installation.

    Thanks



  2. #2
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: condensing unit installation

    Not a good idea, the condenser should always be above the reciever. It allows it to drain properly and stops your reciever levels surging and your condenser to not log liquid. If you install your reciever down under the condensers then you will be alright, mind you the liquid line losses due to the height may cause your liquid to flash if your rise is too great back up to the evaps, in this case you need additional subcooling or a liquid pump.
    Hope this helps
    Last edited by 750 Valve; 28-09-2007 at 05:08 PM.
    ...and she said "give it to me you big fridgie"

Similar Threads

  1. TXV sizing with a larger condensing unit
    By kengineering in forum Technical Discussions
    Replies: 13
    Last Post: 27-08-2007, 10:44 PM
  2. M I T S U S H I T A ac unit with no condensing unit
    By Chinua in forum Air Conditioning
    Replies: 2
    Last Post: 28-07-2006, 06:54 PM
  3. York/Bristol Condensing Unit
    By Abe in forum Commercial
    Replies: 1
    Last Post: 03-02-2003, 07:46 PM
  4. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •