26-09-2007, 11:43 AM #1
Variable Speed Screw Hz
Just wanted to get peoples experiences with "overclocking" a semi hermetic screw compressor above its rated Hz, or any semi hermetic compressor for that matter (although I doubt you'd do it to a recip).
Have you ever seen a semi hermetic screw compressor running above 60Hz? Do you guys in the UK frequently run them up at 60Hz? Any issues encountered, oil, disch temps
I have been discussing this with a manufacturer which claims to have run comps as high as 75Hz if the drive and motor will allow it to.
I am contemplating running up to 60Hz, thats up from 50Hz which is our normal line supply, but had it mentioned to me we may even be able to go higher, what do you guys think?Last edited by 750 Valve; 26-09-2007 at 11:46 AM. Reason: coz i can
...and she said "give it to me you big fridgie"
-
28-09-2007, 07:28 PM #2
Re: Variable Speed Screw Hz
I have seen screws running up to 75 hz, but they are Bitzer open direct drive. Never had any problems.
-
29-09-2007, 03:59 PM #3
Re: Variable Speed Screw Hz
Thats the type I'm talking about, except the HSK semi screws. Cheers, thanks for the info.
...and she said "give it to me you big fridgie"
-
07-10-2007, 10:31 AM #4
Re: Variable Speed Screw Hz
Bitzer semi hermetic screw, HS 53 & HS 64 series can run up to 75Hz, for HS 74 series can run up to 67Hz
The minimum is 20Hz. As standard, you set in between 25Hz to 60 Hz is pretty safe.
-
09-10-2007, 07:02 PM #5
Re: Variable Speed Screw Hz
the range of speed in Hz for semi hermetic screw compressor is depend on it's motor size, for example Bitzer semi hermetic screw HS series ( HSK or HSN ) up to 60 HP nominal can run up to 75Hz, for above 60HP, the higher range is up to 67Hz or 4000 rpm.
I also know Bitzer even have hermetic screw about 15HP nominal size with special motor can run up from 20 to 87Hz, specially design for train a/c application
-
10-10-2007, 09:19 AM #6
Re: Variable Speed Screw Hz
Thanks for the info JFK, we're running between 30hz and 60hz but if needed we have the cond capacity and motor capacity to run to 75hz, we do not require it though.
...and she said "give it to me you big fridgie"
-
10-10-2007, 09:26 PM #7
Similar Threads
-
VSD on screw machines
By Mike Hopkins in forum New TechnologiesReplies: 14Last Post: 20-02-2011, 12:10 AM -
advantage of twin screw compressor over single screw compressor
By azzah in forum New to REReplies: 7Last Post: 23-09-2008, 09:24 AM -
Can we use a VFD for reciprocating comp.
By ukram in forum FundamentalsReplies: 44Last Post: 14-01-2007, 07:44 PM -
Variable speed screw compressors
By Friobernal in forum Industrial CompressorsReplies: 1Last Post: 14-11-2004, 09:28 AM -
Variable speed fridge compressors
By Brian_UK in forum Air ConditioningReplies: 5Last Post: 18-05-2002, 11:37 PM