    Commissioning City Multi



    We are commissioning a PUY series City Multi. Normally we woud use the auto address function but the spec dictates that CMFRTTCB interface boards are installed.

    According to the tech manual the auto address function does not work when using these boards and they should be manually addressed but it does not expand on the manual address procedure.

    Do you simply address the fan coils by using the 2 rotary switches or is it more complicated than this?



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Commissioning City Multi

    Well that depends! Outdoor should be 51. First indoor 001 and remote controller to that indoor 101, second 002 and RC 102 and so on. BC controller 52, but you're not using one.

    Setting is indeed with the rotary switches. Look close at which is the ten's and which the second digit.

    If you need any more, I have a service handbook!

  3. #3
    Join Date
    Jul 2004
    Location
    Scotland
    Posts
    51
    Rep Power
    20

    Re: Commissioning City Multi

    Thanks for the feedback.

    With regards to interface cards do they need an external power supply. The supplied literature is a bit vague.

    Thanks

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Commissioning City Multi

    If by interface cards you mean the printed circuit boards on the indoor units, then yes you'll have to supply them with 240V. The connection is next to the communication terminals!

  5. #5
    Join Date
    Jul 2004
    Location
    Scotland
    Posts
    51
    Rep Power
    20

    Re: Commissioning City Multi

    We are using the additional CMFRT BMS interface cards.

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Commissioning City Multi

    I'm not familair with the CMFRT BMS, but if it's like a LMap, then I gues it needs it's own supply.

Similar Threads

  1. Need input on City Multi
    By TDfromNY in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2006, 03:31 AM
  2. r22 city multi problem
    By mr slim in forum Trouble Shooting
    Replies: 3
    Last Post: 11-01-2006, 06:27 PM
  3. Mitsi City Multi Compressor Death
    By aeb200 in forum Air Conditioning
    Replies: 4
    Last Post: 16-11-2005, 09:10 AM
  4. Mitsubishi city multi
    By techni in forum Air Conditioning
    Replies: 2
    Last Post: 04-07-2005, 05:37 PM
  5. city multi
    By techni in forum Air Conditioning
    Replies: 1
    Last Post: 30-06-2002, 11:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •