    Are there any guidlines for ventilation in occupied rooms? I've come across various schemes that seem to vary in approach.

    Some rooms I have been asked to look at will probably need a\c but I am concerned about ventilation as I feel a\c will not address this issue and despite feeling cooler, the room occupants are still going to fall asleep after lunch...

    The rooms are between 5.5 to 3.8 kW cooling duty each and room volumes 63 cu metres (18 occupants max) to 38 cu metres (12 occupants max), all sitting.

    One other room has around 11 kW cooling duty, 25 occupants for a 150 cu metre volume.

    My gut feeling is fresh air ducted in via a central a\c unit but as building is already up and occupied, and costs tight, it may hit the "How Much!!!! barrier".

    As this problem came up as an afterthought after the rooms got thrown up in a hurry, it may be fans in the walls of each room as a starting point and split or multi-split units.

    Thanks

    Steve



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Ventilation

    Hi Steve

    If you look on page 23 you will see that it is 10 l/s/person. Don't forget to add the fresh air load to your cooling equipment.

  3. #3
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    38
    Rep Power
    0

    Re: Ventilation

    Quote Originally Posted by SteveDixey View Post

    Some rooms I have been asked to look at will probably need a\c but I am concerned about ventilation as I feel a\c will not address this issue and despite feeling cooler, the room occupants are still going to fall asleep after lunch...

    Steve
    That beats all calculations and guidelines The upper limit of ASHRAE comfort zone is 27C (this is subjective and 25C maximum should be ok at RH NMT75%). If you want to remove 11kW with OA then you have to have a temperature difference of about 19C considering 0.47cu.mtr/sec.

    The temperature difference should be about 10C if you consider load from people alone (which is about a ton)

Similar Threads

  1. Underground ventilation for -25°C Freezer room
    By edisonconsult in forum Commercial
    Replies: 7
    Last Post: 02-11-2010, 05:44 PM
  2. Paint Shop Ventilation
    By hlacviet in forum New to RE
    Replies: 2
    Last Post: 09-08-2007, 11:13 PM
  3. ventilation
    By jack smith in forum Commercial
    Replies: 4
    Last Post: 31-07-2007, 11:38 PM
  4. Salt Air Ventilation - Slightly Off Topic
    By Brian_UK in forum Air Conditioning
    Replies: 7
    Last Post: 30-09-2006, 06:15 PM
  5. ventilation for laundry
    By watana in forum Fundamentals
    Replies: 1
    Last Post: 29-04-2002, 06:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •