29-08-2007, 11:50 AM #1
Goodman 2.5 Ton A-Coil pulsing.
Hi All
Got the duct work done for my A coil install, silfosed the lines, nitrogren pressure tested and gave it a good 30 minute vacuum. Upon start up, the dishcharge at the A-Coil give a noticable "pulse". Enough for it to make the line move. Right where the discharge changes to the orface tubes there is a built in bracket to hold the discharge line/orface tube assembly to the ductwork, this is something I have not noticed on any other installs. The system is r-22, pressures are 80/140 at about 17 celsius ambient temperature. 50 feet from condenser to A coil. The system is cooling just fine, the compressor sounds very smooth. Any ideas on what would cause this pulsing?
Thanks
-
31-08-2007, 01:10 AM #2
Re: Goodman 2.5 Ton A-Coil pulsing. solved
Low refrigerant was the cause, added 5 pounds, ouch. Then pulsing stopped. Posting this to help anyone else with the same problem.