    DIY install???



    hi,
    I've today been asked to install 2 "DIY" units, looking through the destructions and the method suggested for removing air and moisture is bizzarre, apparently i dont need to vac out or pressure test, but couple up the pipes (not sealed quickfits but pre flared copper ends)open the lp valve from the condenser for 6 seconds then close it then check for leaks with soapy water, then (taken from instructions)
    push in the ‘tyre inflator’ style valve on the T-branch valve (SIDE OF BOTTOM VALVE) for 4 – 5 seconds using a screwdriver or similar, to expel the air in the pipe-work.
    This cant be legal can it???



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: DIY install???

    No, it can't.
    At least not here in UK.

    Who sold this unit?

  3. #3
    Join Date
    Apr 2007
    Location
    Lancs, UK
    Posts
    21
    Rep Power
    0

    Re: DIY install???

    not sure, the client has had these units in storage, allegedly they are new and unused & admittedly they look it, they have some kind of spacey logo on the condenser.

    are these kind of "DIY" installs common place in the uk these days i wonder.

  4. #4
    Join Date
    Mar 2007
    Location
    england
    Age
    45
    Posts
    78
    Rep Power
    18

    Re: DIY install???

    Iv seen some units like this on ebay from china made by a company called nett. They say they are DIY just to sell them.

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: DIY install???

    Well concidering they're using R-134a & R-152a as air duster whats some more refrigerant to the atmospherre <_<

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: DIY install???

    Just remember that if you are installing them, as an electrician, you will no doubt be issuing a suitable certificate about your installation.

    The customer needs this to go with the building records.

    How do you explain that you have installed equipment against current standards on your documents?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: DIY install???

    Quote Originally Posted by malcoa View Post
    not sure, the client has had these units in storage, allegedly they are new and unused & admittedly they look it, they have some kind of spacey logo on the condenser.

    are these kind of "DIY" installs common place in the uk these days i wonder.
    Is the logo blue?

  8. #8
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: DIY install???

    If you install them as per the instructions then you are breaking UK law, and I would imagine many other countries laws as well.

    If you dont install them then some "cowboy" will, I would do the job but in such a way as to comply. I would also let the customer know that there is a problem with the instructions.

    These aren't by any chance B&Q items?


    Paula

  9. #9
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: DIY install???

    Malcoa

    If you have a digital camera, posting some pictures may help us too visualise this particular product

    Any chance of getting some?

  10. #10
    Join Date
    Apr 2007
    Location
    Lancs, UK
    Posts
    21
    Rep Power
    0

    Re: DIY install???

    the logo was/is blue, my intention is to comply with the standards, i`ll try to get photo's if the job goes ahead but its likely to be a week or two away, never looked at a b&q m/c so i cant say

  11. #11
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: DIY install???

    I think I know the units you are talking about. They sound like Tekion units. The old 407c units had a blue logo which if you looks closly is a map of asia. The newer 410a units have a green logo.

    The instructions are same as you describe. Over here we have similar units which can be bought in DIY shops. There is a sticker on the side of the condenser with the model and serial etc, and instructions on how to purge the lines for "first time use". I can´t remember which brand it is, there are so many over here lately, but it´s either Ventop or Thor.

  12. #12
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: DIY install???

    Why go with the destruction manual or instructions?

    Do the job as per qualified technician, first pressure test (hopefully with dry nitrogen) and then vacuum and open up the valves on the condensing unit!

    Old Refrigeration Technicians never die, they just leak out!

  13. #13
    Join Date
    Jun 2006
    Location
    USA
    Posts
    204
    Rep Power
    18

    Re: DIY install???

    Quote Originally Posted by Paulajayne View Post
    If you install them as per the instructions then you are breaking UK law, and I would imagine many other countries laws as well.

    Paula
    Venting the refrigerant to purge the lines isn't legal here in the US either. Many of the units on eBay are R22 units, not R134A.

    The problem is many of these units are not fitted with proper service connections either, making it a bit of a problem to connect your vacuum pump to do it right.

  14. #14
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: DIY install???

    With apologies to readers anywhere other than UK..... When the B&Q units (Airforce) first appeared about 2 summers ago I was horrified that there was a clear implication contained within the advertising that this was a DIY job, although there was some rather vague mention that the purchaser might need professional help. I immediately wrote to the manager of my local store (no use trying to confront him/her as they are rarely there) and outlined the considerable risks involved to the purchaser, his family, neighbours and the environment. I was 'rewarded' with an immediate telephone call, the gist of which was that the manager had no idea of the potential problems, and he felt sure his company did not either. He promised that he would look into it and forward my letter to HO without delay...

    2 years on nothing has changed.. B&Q are still selling the kit !

  15. #15
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: DIY install???

    .

    I think that the B&Q Airforce units are on the way out.

    Firstly there’s a strong indication from the Govt and the EU commission that the new F Gas Regulations prohibiting the sale of products containing controlled substances (F Gases) and the installation by non-qualified individuals (the public) will be extended to cover these do-it-yourself units, even though they are not equipped with service valves.
    The true extent of the Regulation is expected to be finalised later this year and it’s a loop-hole to be plugged.

    Secondly, despite the crappiest summer in years and disastrous rain in some parts of the country (UK, that is), the presence of domestic A/C is still relatively buoyant, but in my local B&Q last week the Airforce units were piled on the end of a row and were under price-reduced offer.

    B&Q can probably see the writing on the wall.

    Incidentally, B&Q are still in breach of another law, or at least they were in the branch I visited last week. This A/C product requires an energy efficiency label to be displayed at the point of sale (just like washing machines and fridges, A, rating good to G rating, bad).
    I have yet to see one on display in B&Q as they should be.

    .

  16. #16
    Join Date
    Jul 2007
    Location
    New Zealand
    Age
    43
    Posts
    5
    Rep Power
    0

    Thumbs up Re: DIY install???

    In NZ there is currently a huge problem with chinese units that have been imported and are being sold through DIY wholesalers. There are now strong requirments to meet prior to importation of these units.
    The company i work for has recently been contracted to follow behind so called certified installers and clean up there mess of improper and poor installations. My biggest gripe is hearing how good some electricians are then having them allowed to install air conditioning units with out any basic refrigeration training.
    ELECTRICIANS AND BUILDERS SHOULD STICK TO WHAT THEY KNOW AND LEAVE A/C AND FRIGE TECHS TO DO WHAT THEY KNOW!

  17. #17
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: DIY install???

    Quote Originally Posted by Argus View Post
    .
    Firstly there’s a strong indication from the Govt and the EU commission that the new F Gas Regulations prohibiting the sale of products containing controlled substances (F Gases) and the installation by non-qualified individuals (the public) will be extended to cover these do-it-yourself units, even though they are not equipped with service valves.
    The true extent of the Regulation is expected to be finalised later this year and it’s a loop-hole to be plugged.
    How does this relate to the sale of central heating boilers by B&Q, and others, Argus, as these must surely be covered by CORGI?
    Or is it just the installation of such appliances that is covered by legislation?

  18. #18
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: DIY install???

    Quote Originally Posted by frank View Post
    How does this relate to the sale of central heating boilers by B&Q, and others, Argus, as these must surely be covered by CORGI?
    Or is it just the installation of such appliances that is covered by legislation?
    I’ll admit here and now that I’m not an expert on the laws of central heating, but my understanding is that when you buy a boiler, you do just that.

    There’s nothing to stop you buying it, fixing it to the wall and fitting the WATER pipes – but NOT working on the gas side.
    The offence under the gas regulations and the various ACOPs is that of working on live gas when not qualified or certified.
    (If there’s a better take on the subject by someone more knowledgeable on this subject, we’d like to hear of it)

    The F Gas regulations on the other hand seek to restrict the sale of products containing controlled substances (F Gases) and the subsequent use of F Gas in the terms of the F Gas regulation.

    The problem with the new F Gas regulation so far is, in my opinion, contained in the inadequate drafting in the first place that leaves a number of areas and questions unaddressed - typically, the question of DIY units.

    .

  19. #19
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: DIY install???

    .

    Here's the A/C department at my local B&Q.

    Note the space-saving outdoor unit already conveniently piped up.

    In fact, they are selling it all off with a 33% reduction and this end of line bin is all there is.

    .
    Attached Images Attached Images

  20. #20
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: DIY install???

    Note the space-saving outdoor unit already conveniently piped up.
    And correctly positioned?

  21. #21
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: DIY install???

    Quote Originally Posted by Sanderh View Post
    And correctly positioned?
    Absolutely!

    It's in tip-top condition.

    You won't find a better example on the planet.

    .

  22. #22
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: DIY install???

    Quote:
    Originally Posted by: Sanderh

    And correctly positioned?


    Absolutely!

    It's in tip-top condition.

    You won't find a better example on the planet.
    And why didn't any of you tell me this any sooner, would have saved me a bundle of work!!!!!!!!!!!

  23. #23
    Join Date
    Jun 2007
    Location
    Leicester
    Age
    50
    Posts
    39
    Rep Power
    0

    Re: DIY install???

    I think there are still plenty of dodgy ac installers who still use the purge method am sure some work where i do..........

Similar Threads

  1. Do Should we install units customer has brought off ebay?
    By chilly in forum Air Conditioning
    Replies: 65
    Last Post: 21-01-2008, 10:32 PM
  2. Aussie Split Install
    By FreezerGeezer in forum Air Conditioning
    Replies: 24
    Last Post: 03-08-2007, 12:07 AM
  3. New install with pump down??
    By justchillin' in forum Trouble Shooting
    Replies: 2
    Last Post: 23-09-2006, 11:42 AM
  4. Advice on Daikin install
    By classact in forum Air Conditioning
    Replies: 0
    Last Post: 14-06-2006, 12:19 AM
  5. How do you install a central air system?
    By Industrial tech in forum Air Conditioning
    Replies: 1
    Last Post: 26-05-2003, 06:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •