    Hi everyone!
    Can someone please help!!
    I have been called to a Williams fridge with an L'Unite hermetique compressor, capacitor start induction run.Someone has had a butcher at it and blown the current relay that pulls out the start winding. I have replaced the relay but it keeps cycling. I am not sure if the compressor is siezed as it has a history of being recharged at least twice a year and may have no oil. I also noticed that the common terminal is conected to a live via a clixon and control. The start terminal to neutral through capacitor and run terminal to neutral through coil of current relay.
    Am i wrong in saying that the common should be coneected to neutral and remaining pins to live!
    Not to sure my book shows a diagram but supply labeled L1 L2 not L N.
    Apr 2001
    2,099
    27
    Re: L'Unite hermetique wiring
    Quote Originally Posted by Chilly willy View Post
    Hi everyone!
    When you say cycling, how long does the cycle last?
    Is it a few seconds, or longer
    May 2006
    china
    98
    Hi, chilly. Basing on your information, this compressor's wiring connection may be CSIR type. So, Common terminal needs to connect L line via a overload protector. Other teminals are connected correctly.
    Jul 2007
    Australia
    1,845
    when you say cycling, you mean compressor humming and not doing anything until the klixon goes open circuit, or do you mean it gets running and underway for a few seconds then cuts out?
    What type of amps is it drawing?
    Have you checked the capacitor?
    Chilly willy Guest
    Checked capacitor and its out by a couple of micro farrads which seems ok! It is the actual current relay that keeps cycling for may be a second or so every thirty seconds, Compressor dont start run though, getting voltage there so must be siezed. My clamp meter snuffed it so can't see what it's pullin.
    Thanks for responding to my post anyhow!
    Apr 2006
    Guess
    61
    Not wrong but not necessarily right.
    With Hermetique's it doesn't matter which way you connect the phase or the neutral so long as the wiring is right.
    If it was easy everyone would do it.
    Mar 2007
    34
    get a megger on the compressor and see if the comp windings are blown. possible because the unit is a leaky the compressor has been running along time with little or no fridge in, sound like comp has had it!
    Oct 2003
    5,630
    34
    Quote Originally Posted by Ireland View Post
    We're speaking abouth AC current, so it doens't matter at all, for any electrical device.
    You're sure the right current relay was installed?
    Not every current relay suits for the job.
    Try this once (if compressor isn't already replaced ) connect the compressor via an AC wall socket on the Live (clixon) and the Run (right under) Then connect with an isolated wire or with a pinch tool the Run with the Start (so right under with Left under) for a second or two and look what's happening.
    A current relay only switches when the current through the windings goes high enough to close the contacts.As soon running current drops, the relay opens.
    The phenomena you describes can have two reasons: wrong or bad relay and/or a high loading compressor.
    I bet you have installed a wrong current relay, one for a smaller compressor.
    Aug 2005
    northampton
    64
    9
    Cool Re: L'Unite hermetique wiring
    sounds like the start windings on the comprssoer are ok but when the run windinding is switch on it is Useless
    Get an ohmeter check the windings two small values should add up to the largest value give or take a bit
    megger the comprssor out to check and shake it !!
    if it rattles it should be free if not could be part siezed.
    Also look at the drier if it has one has that been changed ! why ?
    ! had one of these with a blocked drier and it ran up pumped and could not keep going cleared blockage ran ok without tripping the klixon out
    williams fridges are prone for leaking on the evaporatoers check that to because your compressor could be running and running
    As r134a gets llow on pressure it actually nearly reaches freezing conditions before it goes in to vacuum
    your client thinks things are ok and boom another comprssor goes up the swanney.
    Chilly willy Guest
    Smile Re: L'Unite hermetique wiring
    Hi everyone thanks for all your help!
    Problem now sorted! Customer explained to me that prior to my visit the system had been getting topped up with gas by another engineer, on my first visit I noticed current relay blown so I replaced it with exact same relay which kept cycling in an out as I mentioned, Checked all windings which all added up so not open or shorted. Decided to change compressor and recovered about twice amount of gas as on data plate, Changed drier and compressor and hey presto, she's a runner. Thank you all for your suggestions it's nice to know theres help when you need it!! Live long and prosperous!!!!
    Apr 2007
    lancashire england
    64
    36
    jesus christ it doesnt get anymore basic glad your not workin on my equipment
    Oct 2003
    5,630
    34
    So, changing the compressor wasn't needed at all, just recovering some gass
  1. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Last Post: 25-09-2009, 06:24 PM
  2. l'unite hermetique R12 Condensing unit
    By airefresco in forum Commercial
    Last Post: 08-02-2008, 09:08 PM
  3. L'Unite Hermetique compressor
    By iceman007 in forum Commercial
    Last Post: 27-06-2004, 08:15 PM
  4. Wiring Diagrams
    By Abe in forum Trouble Shooting
    Last Post: 02-12-2001, 10:19 PM