    Dec 2006
    dd
    5
    low discharge tempeeature
    the compressor is twin screw type,Evaporationg Temperature=-3degC,Condensing temperature=43.5degC.But the discharge tempeeature is 48 degC! it should be more than degC,isn't it?
    Jul 2006
    Copenhagen
    Re: low discharge tempeeature
    What refrigerant?. I would say too much refrigerant on the system
    Mar 2006
    Malaysia
    48
    233
    It sounds u u have refrigerant liquid slugging in ur screw compressor cools down the the discharge temperature to this degree. So it is better to check out the TXV bulb position or its size (perhaps it is oversized) or there is over charging in ur system. What is the sort of ur oil cooler system?.
    May 2006
    India
    82
    1,013
    The possibility of overcharging is more. Please also check the TEV wether it has been properly selected and if the same is operating.
    Apr 2007
    Phillipine
    22
    Where is you location cause the equipment already size up to 43.5C and you have 48C discharge temp. also the refrigerant use, do include the oil. It is unusual to have that high temp. and still have high discharge temp. The factor is the impurity of both oil and refrigerant. The moisture inside the compressor and the system. Also the dirt on the condenser if it is aircooled clean it with water and if it shell and tube scrub it.
    Jul 2007
    Australia
    1,845
    Quote Originally Posted by mohamed khamis View Post
    Wouldn't the compressor suction temp tell you this? Sticky frost on the suction line and no superheat at the compressor?
  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Last Post: 25-04-2010, 07:43 PM
  2. Screw discharge cooling
    By Volnei in forum Industrial Compressors
    Last Post: 05-11-2008, 09:24 AM
  3. Oil Leak in NH3 Discharge Line Flange
    By NH3LVR in forum Industrial
    Last Post: 26-05-2007, 09:15 PM
  4. Exploded discharge line
    By Peter_1 in forum Industrial
    Last Post: 05-05-2004, 09:47 PM
  5. Discharge Desuperheating Good or Bad?
    By Calvin Becker in forum Technical Discussions
    Last Post: 31-05-2003, 11:42 PM