17-07-2007, 09:38 PM #1
short of gas symtoms?
hi, just running this by you guys<, an engineer i work with was telling me that icing back to the compressor are signs of lack of refrigerant on an r22 split wit a setpoint of 18, was i right in disagreing with him by saying that if there was a lack of refrigerant you would be getting abnormal tempartures after expansion and posssibly get ice on parts of the heat exchanger and then in turn get high superheat! too me icing up too comp would indicate no airflow, dirty coils etc also i heard someone a mention a high latent heat load can cause this problem... can someone give me there opinions?
cheers
-
17-07-2007, 10:59 PM #2
Re: short of gas symtoms?
Start with your thoughts first.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
17-07-2007, 11:29 PM #3
Re: short of gas symtoms?
was i right in disagreing with him
Everything you said is pretty much true.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
18-07-2007, 03:24 AM #4
Re: short of gas symtoms?
Hi there,
Here is the lack of refrigerant symptoms:
1- Low LP
2- Low HP
3- High super-heat
4- Low sub-cooling
5- Bubbles in the sight glass
Sub-cooling is the best indication.
When suction line is frosted then this could be from :
1- The suction gas temperature is below 0°C. Means the suction pressure is low, for whatever reason.
2- Liquid flood back.
Lack of refrigerant is very simple to diagnose.
CheersEven Einstein Asked Questions
-
18-07-2007, 08:12 AM #5
Re: short of gas symtoms?
thanks for replys lads, any ideas about a high latent heat load? cant really get my head around it....from what take from it is if the there humidity to remove from the air it takes so much watts of cooling to change condition of air and struggles to take down temp, any ideas on how this would cause icing of suction?
rgrds
-
18-07-2007, 08:34 AM #6
Re: short of gas symtoms?
No....When the system is operated under high latent load compared with the sensible the moisture drain off is only increased and no possibilities for frost to be existent on the evaporator coil unless the system is much overdesigned and the evaporatung temperature is below zero and it is very scarce to occur.
Regards
-
21-07-2007, 04:34 AM #7
Re: short of gas symtoms?
high latent heat load is the amount of moisture the load contains. on container reefer cargo certain loads are brutal for this ie. herring roe and certain frozen fish. both are packaged in a brine solution which is a water and salt solution. herring roe is -10c and will consistantly ice up evap coils which blocks air flow hence ices up compressors etc... frozen fish -23c does the exact same thing. this product makes it difficult to reach setpoint sometimes defrosting every 45 mins to 1 hour to achieve any results. alot of nuisance service calls but otherwise easy money!!
Similar Threads
-
Compressor short cycling....
By sbessettejr in forum Trouble ShootingReplies: 10Last Post: 02-04-2007, 05:09 PM -
Short Cycling blues & low pressure control switch
By mccoolair@yahoo in forum Supermarket RefrigerationReplies: 14Last Post: 09-04-2006, 09:28 PM -
Aircon strategy for a school hall with short lease?
By mamborambo in forum Air ConditioningReplies: 13Last Post: 25-02-2006, 08:47 AM -
Walk in Cooler (short cycling)
By Brandon in forum Trouble ShootingReplies: 11Last Post: 05-05-2003, 11:43 AM -
The slow leak, the intermittant short...
By Dan in forum The Trail of TearsReplies: 16Last Post: 14-07-2001, 03:16 AM