    We are designing a freezer room located on ground gloor ( 63 Mtr x 15 Mtr x 9Mtr high). Due to the huge size we intend to use underground ventilation to prevent freezing. Can anyone guide on underground ventilation?



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Underground ventilation for -25°C Freezer room

    I would not have thought that 'underground ventilation' would work.
    Is your idea to have vents running under the freezer room with air blowing through them to stop the floor going too cold?
    Do you not think that the ducts would ice up within 1 day?

    I think a heater mat would be better.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Underground ventilation for -25°C Freezer room

    Quote Originally Posted by edisonconsult View Post
    We are designing a freezer room located on ground gloor ( 63 Mtr x 15 Mtr x 9Mtr high). Due to the huge size we intend to use underground ventilation to prevent freezing. Can anyone guide on underground ventilation?

    Hi edisonconsult

    normally we would use 3/4 inch water pip buried in the sub floor with waste heat from the compressor discharge used to heat a glycol/water mix, pumped around the pipes.

    For your method you would need to elevate the sub floor level to above the finished ground level outside, then bury 6 inch concrete pipes every foot or so in the sub floor, running accross the short length.

    This will work, provided the local ambient does not go below freezing for more than a few days at a time. ie it would work in the uk.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Underground ventilation for -25°C Freezer room

    Several of the freezers I have seen using underfloor ventilation use 6" PVC pipe. The exterior pipes usually rise up about 2 feet or so above their horizontal position and have reverse traps on them to prevent water entrance from rain.

    Another method is to recover warm air and blow it through the pipes, although this is more compicated than the natural ventialtion system.
    If all else fails, ask for help.


  5. #5
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Underground ventilation for -25°C Freezer room

    We have one freezer in Florida that we are blowing the outside ambient air through 24 6inch pvc 200 feet long, an engineer told us the cfm's that we needed, sized the airhandler for the required cfm's and installed, or glycol through a heat exchanger works well to.

  6. #6
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Underground ventilation for -25°C Freezer room

    Watch out for water condensation in the ventilation piping. They should drain outside or to a low spot inside and fitted with a sump pump or other method of getting rid of the water.

  7. #7
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Underground ventilation for -25°C Freezer room

    Hello Edisonconsult

    According with some paper you should estimated betwenn 2-3btu/ft2 h the heat entering to the cold room througt floor .

    The air pipe should be PVC reinforced.
    They should be installed between 1.2 to 1.6 m wide
    The pipe should be 4" ,6" or 8" diameter acording the lenght
    It will be better located the pipe in the shorter distance
    the pipes should be pitch 0,5 to 1% down
    Each pipe should be independient .The inlet should be protect agains rain water and animals getting in.
    The outlets should drain freely and protect it against animals

    If the arquitecture of the building does not alow you to use independ pipes and you should use a forced air fan than you should follow this tips.
    The pipes should be installed via a manifolds.The inlets and outlets
    The pipes should be pich to just one spot
    The lower spot should have a drain with a siphon to keep a water seal
    All the outlet air could be used to refresh any room like room machinery (as make up air)

    Finelly if you make some calculation of the amount of air you require to keep worm the floor you can verify the mass of air is very small due the moister latent heat. So you should select the fan just to garantee a good velocity of air throught the each pipe.
    I hope this can be helfull for you
    Best regards

  8. #8
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Underground ventilation for -25°C Freezer room

    Hello guys, sorry to re-open such an old post, but I'm looking for info about the design of forced air system. Do you have info or references on how to calculate de CFM's and pressure drop required?

Similar Threads

  1. Freezer Room Defrost
    By Samarjit Sen in forum Commissioning
    Replies: 23
    Last Post: 21-06-2007, 06:16 AM
  2. Misa Kit Freezer Room
    By Abe in forum Commercial
    Replies: 2
    Last Post: 03-01-2007, 09:04 PM
  3. foster compact freezer room
    By Andy AC in forum Commercial
    Replies: 6
    Last Post: 10-08-2006, 10:52 PM
  4. New Freezer Room Panels
    By Abe in forum Legal-Business-Marketing
    Replies: 7
    Last Post: 04-05-2005, 09:43 AM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •