Results 1 to 12 of 12
Thread: R22 to R717
    Sep 2005
    Indonesia
    44
    5
    R22 to R717
    Hello guys,
    I have a problem, maybe some of you have an experience regarding this matter
    We have a R22 Plate freezer complete with liquid separator made from copper
    We want to install the plate freezer in ammoniak system, I already check the plate freezer, it made from aluminium
    I know that i cannot use the separator, and what else that i have to replace ?
    Thank you
    Aug 2001
    1,046
    Re: R22 to R717
    The short answer is, everything.
    May 2006
    India
    82
    1,013
    Re: R22 to R717
    if you are changing from R 22 to R 717, then you have to change everything including the compressor. It is better to install a complete set of R 717 equipments than trying to replace any part.
    Aug 2005
    5,302
    Re: R22 to R717
    Hi Yoga,
    I think you should plan on changing all of the refrigeration system. Converting systems from R-22 to ammonia will create a lot of problems, even if the materials (pipe, condenser, compressors, etc.) are compatible with ammonia.
    I doubt this is the answer you were wanting, but it is the best way to proceed if you want to change to ammonia.
    Sep 2005
    Indonesia
    44
    5
    Re: R22 to R717
    Thank you for your reply
    for your information :
    The platefreezer is just the freezer without compressor and Condensor
    Our customer already have a amoniak refrigeration system with two stage reciprocating grasso compressor, they bought a used R22 platefreezer and they plan to install it in the existing amoniak system
    Apr 2007
    Phillipine
    22
    Re: R22 to R717
    Just replace the equipment with copper material on it. NH3 will corrode it fast. If your system is ammonia upgrade the system of the plate freezer.
    Pennsylvania
    113
    Re: R22 to R717
    In the facility I work in we have converted two tube ice machines and an evaporative condenser from R22 to R717 with little problems.
    Get manufacturer's recommendations, engineering sign-off and hire a competent contractor.
    Luckily for us the equipment itself needed little change. The piping had to be replaced as did the pressure regulators. Thankfully the solenoids were suitable and could be reused with a new set of flanges.
    I think you will see more of this type of conversion in the future. I know, for example, that we have a 1.2mil square foot facility running R22. That facility is being considered for conversion to R717 which would be a very impressive project.
    Aug 2005
    5,302
    Re: R22 to R717
    Converting some individual pieces of equipment from R-22 to ammonia should not pose many risks. If the materials of construction are compatible you will probably be OK. I might suggest rebuilding the solenoid valves and any regulators because of gasket or o-ring swelling that might occur.
    On the other hand converting an entire system is not the same thing and I have heard one real horror story about problems. Let's say it rivaled a similar case of getting CO2 in an ammonia system. Quite the mess.
    Jun 2005
    New Zealand
    58
    34
    Re: R22 to R717
    The materials for the plate freezer itself should be fine as most are designed for ammonia or R22 applications. Obviously any copper items have to go. The biggest issue, IMHO, is the potential for R22 contamination of the ammonia. I had a thermsiphon spiral freezer on ammonia a few years back that somehow got some R22 into into it and it ate throught the aluminum evaporator coil after about 5 years and had to be replaced at the cost of around 50,000E. Be absolutley sure that ALL traces of refrigerant and oil are removed from the plates before installing them.
    Sep 2005
    Indonesia
    44
    5
    Re: R22 to R717
    How to clean the oil and R22 from the plate freezer?
    Is it need liquid chemical ? or just with compressed liquid soap and water?
    May 2006
    India
    82
    1,013
    Re: R22 to R717
    Flush the Plate Freezers with Nitrogen a number of times.
    Jun 2001
    N.Ireland
    1,630
    Re: R22 to R717
    Quote Originally Posted by yoga View Post
    Hi Yoga
    you could flush the plates with warm water, but you would need a lot of heat and a vacumn pump to remove the water. Nitrogen is probably the easy way
    What about the hoses on the plates, the rubber in them will probably fail when you change to ammonia, it is always a good idea to change the hoses as part of your overhaul before starting the plate up.
    Kind Regards Andy
  1. NH3
    By joscon in forum NH3
    Last Post: 30-06-2001, 01:47 AM