    Copeland 50HP Compressor (Low Oil Fault)



    I have a problem with a copeland compressor, cutting out on low oil pressure often. i carried out the following tests:-

    1) clean sump oil strainer
    2) check oil pump pressure ( suction 32psig and oil pump pressure 75psig)
    3) check crankcase heater operation which was normal( no liquid feedback)
    4) normal oil level on the compressor sight glass (normally half)

    compressor have a sentronic oil sensing controller with a sensor connected on the oil pump. i have check the operation of the controller as follows:-

    contact on the sensor closes when compressor running ( basically normal oil pressure)

    contact opens when compressor stops. if the disconnect the sensor cable the contacts are open and the red indicator on the controller lights up indicating low oil pressure and once reconnected with 120 secs the green light ups ( normal oil pressure).

    compressor stops if the leave cables disconnected for more than 120 secs. So basically i have tested everything but problem keeps coming often.

    plz help.



  2. #2
    Join Date
    Jan 2007
    Location
    australia
    Age
    46
    Posts
    49
    Rep Power
    0

    Thumbs up Re: Copeland 50HP Compressor (Low Oil Fault)

    Hi there.. Firstly check the oil pressure and monitor it during running, if the sentronic drops out and you have maintained correct oil pressure then the sentronic is faulty.. I have had a fare amount of experience with the sentronic oil saftey device on commercial fishing vessel's and have found them to be unreliable! my advice is to replace with a danfoss oil failure. Hope this helps!

  3. #3
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: Copeland 50HP Compressor (Low Oil Fault)

    Hi Mr Chilltech

    setrad7791 is right. Watch the suction pressure and oil pressure while the compressor is running, but especially check the sump pressure of the compressor with the oil pump pressure.

    Sometimes if the compressor has worn rings or journals it could affect the oil pump pressure.

    Is this a new compressor?

  4. #4
    Join Date
    Apr 2007
    Location
    London
    Posts
    14
    Rep Power
    0

    Re: Copeland 50HP Compressor (Low Oil Fault)

    Hey mate, depending on the wiring of the control and compressor circuit have found a faulty / intermitant time delay on compressor contactor will cause oil fault, is the compressor part winding?

    Cheers redhot

  5. #5
    Join Date
    Jul 2007
    Location
    New Zealand
    Age
    47
    Posts
    6
    Rep Power
    0

    Re: Copeland 50HP Compressor (Low Oil Fault)

    thanx for ur response.

    this is not a new compressor. i have monitor the suction and oil pump pressure on start up and during operation, its all normal.

    There is no wiring issue as the sentronics mains is wired on normally open contact of the contactor so the sentronic only comes ON when the contactor energises. there is no delay on power feed.

    this compressor is on a rack system at a process plant, the operation of the plant is from monday to friday. so during the weekend the compressors stage out and according to the data we have 99% of the time the fault occurs on monday morning when the process starts.

    there is something happening during this loading of compressor after cold start, which i cannot figure it out.

  6. #6
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: Copeland 50HP Compressor (Low Oil Fault)

    I have had intermitant oil pump failures in rare instances. I can only remember seeing it 3 times in 30 years. A real PITA to troubleshoot. You just needed to be lucky and be there when it happens. You need to be onsite when they start the process up on Monday morning.

    Is this sentronic wired with 3 or 4 wires? I have also seen the 3 wire setup feeding back thru the control circuit causing false failures while the system was off?

    Could the compressor be stalling during startup after sitting for awhile?

  7. #7
    Join Date
    Jan 2007
    Location
    australia
    Age
    46
    Posts
    49
    Rep Power
    0

    Re: Copeland 50HP Compressor (Low Oil Fault)

    My advice.. change the oil failure with a danfoss or mechanical oil failure, it's a small outlay to determine if the problem is with the oil control... I can almost be certain it will fix the problem!
    also make sure you check oil pressure with your gauge fitted to the sump... just incase you have a blocked suction strainer at the service valve!
    Last edited by setrad7791; 04-07-2007 at 03:36 PM.

  8. #8
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: Copeland 50HP Compressor (Low Oil Fault)

    Is the compressor on a pumpdown during standstill over weekends? If not, liquid can floodback to the compressor on Monday morning startup, even with an operational crankcase heater!

    Remember, refrigerant likes to stay at the coldest place in the system, the evaporator.

  9. #9
    sonnyshores's Avatar
    sonnyshores Guest

    Re: Copeland 50HP Compressor (Low Oil Fault)

    I had this problem with a walk-in freezer. The fix was to replace the 3PH contactor , one of the legs was holding in at heavy amp. draw then openning letting the compressor run on two PHs causing the oil presure switch to set a fault. The cooling fan on the compressor is running off of two legs, which weaken the third. Hope this helps
    Last edited by sonnyshores; 25-07-2007 at 03:44 AM.

Similar Threads

  1. lg fridge/freezer fault light on function display board
    By bazza in forum Trouble Shooting
    Replies: 0
    Last Post: 25-02-2007, 03:25 PM
  2. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM
  3. Diplomat 6528 Fault Code
    By Targus in forum Domestic
    Replies: 3
    Last Post: 31-10-2006, 07:43 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •