    Career chiller



    I'm working on this chiller it's winter now, so i need only heating i'v got 160 fan coils with electrical duct heaters .The problem is that many cold water stop valves are leaking so even on heating i'm geting cold air.My question is can i shut water valves cose i need only heating right now?Would that afect system?
    Thanks



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Career chiller

    Quote Originally Posted by wolf View Post
    I'm working on this chiller it's winter now, so i need only heating i'v got 160 fan coils with electrical duct heaters .The problem is that many cold water stop valves are leaking so even on heating i'm geting cold air.My question is can i shut water valves cose i need only heating right now?Would that afect system?
    Thanks
    The quick easy answer is yes close the valves.

    The more complex answer would be if it is winter and only heating is on why is cold water passing through the valves?
    Is the system still in use to chill other sections?
    If it is then isolate the valves local to the coil and you should be fine.
    If the system is not required just shut down the system and isolate a few key valves to prevent heat transfer through conduction.

    Cheers taz

  3. #3
    Join Date
    May 2007
    Location
    Belgium
    Age
    50
    Posts
    87
    Rep Power
    17

    Re: Career chiller

    Quote Originally Posted by taz24 View Post
    The quick easy answer is yes close the valves.

    The more complex answer would be if it is winter and only heating is on why is cold water passing through the valves?
    Is the system still in use to chill other sections?
    If it is then isolate the valves local to the coil and you should be fine.
    If the system is not required just shut down the system and isolate a few key valves to prevent heat transfer through conduction.

    Cheers taz
    The chilled water pumps might be kept running to prevent the outdoor chiller and piping from freezing. Worth checking for glycol before you shut them valves.

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •