    LG UB36NGB boring problem...



    Hi everyone
    Have to repair LG UB36NGB+UU37UEB : non inverter split ducted type r410a, 2 years old.

    1st: the 2 small fuse blown; one on outdoor pcb (3.15amp) and another one from R phase (5amps) suppling the indoor unit from the outdoor side, change them, everything's alright for 1 hour then fired again !!!
    2nd: I've check indoor/outdoor fans, relays, compressors one by one, check the whole control-circuit, etc...
    3rd : change the fuse again, wait for 1 hour and leave...the customer called me 2 hours later " Mr ***** my LG doesn't work anymore, are you sure you're relevant enough ?!!"
    4th: i decide to order new pcb but i'm afraid it will be the same.
    In addition let's say indoor pcb fuse and outdoor neutral fuse from N terminal never failed. See attachment.
    When the problem occurs the circuit breaker goes down as a short circuit fault but not the RCD breaker.
    Strange !!!
    Awaiting for advices, hope HENDRAG will read and help, thanks
    cool#9
    Last edited by cool#9; 09-10-2007 at 05:16 PM.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: LG UB36NGB boring problem...

    Hi cool#9
    From looking at the diagram the fault has got to be on the outdoor unit either the fans, reversing valve, the things labled TP in comp A and B or the wiring to them. why not compare the resistances of the thing you have two of.failing that, you could wire in an inline fuse to each and see which one blows, not very technical.

    Jon

  3. #3
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Hi monkey spanners
    I'm afraid this trouble will lead me to your solution...
    Got to choose lower amps fuse to do it as well...
    Hope someone on the forum had the same problem and found.
    If not i'll maybe modify the machine and explain to my customer it appens only on LG outdoor unit ?!
    thanks so much
    cool#9

  4. #4
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: LG UB36NGB boring problem...

    Can't get my head round this one at all. I think M. Spanners is heading in the right direction with the outdoor unit. Is T/B1 a timeclock alternating the motors after an hour during low loads? However if you have checked all the motors could this be overcurrent on the R phase itself? How is the RCD wired?

  5. #5
    Join Date
    Jan 2007
    Location
    SPAIN
    Posts
    172
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Probably far fetched, but...
    1. fault on Signal line [3]
    2. Check S, T and N lines if R for some reason has a higher resistance (e.g. faulty contact in circuit breaker) the current imbalance will run through the fuses into other parts and blow the fuses.
    Corrosion, loose screws, irregular vibration, wire loose, shorting winding on compressor could also lead to this irritating irregular trrouble.

  6. #6
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Hi Cool 9


    Not familiar with this kit but heres my thoughts, I am tending to lean in other directions after reading this, the black and white wires after CM comp conection on the PCB i assume are the run signals for the compressors that pass through the compressor thermal trip (normally closed) then through the secondary protective device / timer (Not sure what that is but is also normally closed) and finally onto the coil of the contactor (a1) to energise it and bring on the compressors. I would expect a fuse to blow instantly on compressor demand if there was problem with these as they dont draw much current and an electrical short circuit would be needed to blow fuses.
    The condenser fans how ever draw current from this fuse so i am leaning towards them, i would look at the capacitors to see they are ok as if they are tired you may be getting intermitent starting or high current draw on there start up. also one of the fans may have a dry bearing so run ok when cold but after a while over heat and swell up making it harder for the fan to spin also causing excessive run current. Maybe indepent fuses on each fan maybe a good idea.
    One other thing to consider, has the unit got a condensate pump fitted and wired off the indoor isolator, if so this could also have a short circuit thats causing fuses to blow as the short tracks back through the electrics.
    After looking at the above and also what others have mentioned i would also be ordering a new PCB.

    Intermitent faults..........dont you just love'em.........Not..!!!!!!!!. good look with it cool9.

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: LG UB36NGB boring problem...

    Just thought of a problem i had with a 3ph fan motor. the thermistor in the windings (wired into control circuit) shorted out to one of the phases suppling the motor, this blew the control circuit fuse as it was on a different phase (415 across control circuit) is the thing labeled "TP" in the compressor? Short could also be in the wiring.

    Jon

  8. #8
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Hi thanks everyone for suggestions.
    Coolments: there's no pump indoor as it's an option for UB 36 unit. I'll check outdoor fan capacitor also.
    Jon: i'll check the wiring of control circuit that follow power circuit, maybe an insulation problem with the power cords of the compressor or something like that...
    Momo and Contactor: i'll follow advices, the RCD is above the airconditionner circuit breaker.

    I forgot to tell you the system run non stop and rarely cut by thermostat off due to poor installation capacity so i think it maybe link with a compressor overload and/or overheat...
    ok, i'll go back to this problem before i get a new pcb and try electrical test with the actual pcb, helped by your advices ive a new motivation to go ahead !!!
    rgds
    cool#9

  9. #9
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: LG UB36NGB boring problem...

    Are the contactors for compressors in good condition?
    Possible arcing?
    Check contactors when operating by carrying out mV test across contactor. All readings should be within reasonable balance of one another.

    Regards
    Jase

  10. #10
    Join Date
    Jan 2007
    Location
    UK
    Age
    53
    Posts
    72
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Hi the problem is with the indoor unit or the 4 way valve or the outdoor fan motors. Assuming both fans are running and the beast is in cooling it wont energise the 4 way valve (heating) but if its switching over this could be the problem. On the indoor there is not much to go wrong the pump runs all the time the compressor is running in cooling but doesnt run in heating and the fan is on most of the time. Its a wierd one this if you get this in time call me tomorrow on 08708720791 option 4 we will sort you out.

    Hope we can help

    regards

    hendrag

  11. #11
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Hi Hendrag and glad to meet you on the forum again !

    The system runs only in cooling mode and there's no additionnal pump in the UB36NGB (as it is optional).
    I remind you the indoor fuse never blown...
    Next days i'll test again the whole parts and of course i will tell what i found (i hope so).
    Thanks for your calling invitation but before i've to be sure it's not a simple eletrical part failure...
    rgds
    cool#9

  12. #12
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    hi,

    to me it looks like an indoor thing,transformer maybe..however why not try dry running everything for an hour i.e...disconnecting compressors,fans,4 way valves and just have the control work and maybe put an amp meter round the cable see what been pulled through that cable...

  13. #13
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: LG UB36NGB boring problem...

    Hendrag - what is T/B1? Is there a guide available for LG wiring diagram abbreviations?

    Thanks

  14. #14
    Join Date
    May 2007
    Location
    Reading
    Posts
    8
    Rep Power
    0

    Re: LG UB36NGB boring problem...

    Hi, the problem sounds like it is almost certainly to do with the Outdoor Unit control side wiring.
    Check the Control wiring from CN_Comp to the Compressor. In the past I've seen abrassion on these wiring looms where they rub against the discharge pipework and intermittently short out.

    Rgds.
    Mac1

  15. #15
    Join Date
    Jan 2007
    Location
    UK
    Age
    53
    Posts
    72
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    its a shot in the dark but intermittant faults are the hardest to fix. if the compressor power leads rubs against the hot pipework the insulation wears through and the unit shorts against the pipework . its a bugger to find unless there is visible damage to the insulation/ pipework. Check all the wiring to the compressors to see if this has happened.

    keep us posted on what you find

    regards

    hendrag

  16. #16
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Quote Originally Posted by Contactor View Post
    Hendrag - what is T/B1? Is there a guide available for LG wiring diagram abbreviations?

    Thanks
    In my opinion that mean Terminal Block 1 for commun neutral wires, but what's exactly above with EOCR-A and EOCR-B ?

  17. #17
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Quote Originally Posted by hendrag View Post
    its a shot in the dark but intermittant faults are the hardest to fix. if the compressor power leads rubs against the hot pipework the insulation wears through and the unit shorts against the pipework . its a bugger to find unless there is visible damage to the insulation/ pipework. Check all the wiring to the compressors to see if this has happened.

    keep us posted on what you find

    regards

    hendrag
    Hendrag, and everyone
    I've find today insulation problem of the "A" compressor leads (white insulation tape ) against the low pressure copper tube ! It also created a small hole in the pipe and then refrigerant leak, never had it before on supposed cold surface pipework !
    I'll try to put pictures on line next days.
    The system runs well now but an expensive work for the customer...
    Kind regards
    cool#9

  18. #18
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: LG UB36NGB boring problem...

    Hey Cool, thanks for the update.

    Cables shorting (arcing) on pipes are not unique to LG, I've had it on several makes before. It is often the power supply cabling that has been run in the wrong place and trapped when the covers go back on.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  19. #19
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Quote Originally Posted by Brian_UK View Post
    Hey Cool, thanks for the update.

    Cables shorting (arcing) on pipes are not unique to LG, I've had it on several makes before. It is often the power supply cabling that has been run in the wrong place and trapped when the covers go back on.
    Thanks but can't accept it appens on the cold gas pipe...
    See the pictures
    rgds
    cool#9
    Last edited by cool#9; 09-10-2007 at 05:16 PM.

  20. #20
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Hi COOL#9, that looks nasty!
    Careful with "admettre" because I think you meant accept, but "admit" here means avouer (I hope my spelling is correct)
    Maybe after an hours running the humidity from the condensation on the cold pipe was creating the short to the wire.
    Where abouts are you btw I'm near Marseille.

  21. #21
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Quote Originally Posted by expat View Post
    Hi COOL#9, that looks nasty!
    Careful with "admettre" because I think you meant accept, but "admit" here means avouer (I hope my spelling is correct)
    Maybe after an hours running the humidity from the condensation on the cold pipe was creating the short to the wire.
    Where abouts are you btw I'm near Marseille.
    Hi expat
    So glad to meet a new french on RE forum ! Now we are two !!!
    Thanks for the word correction, i'll take english lessons in next september.
    I live near Monaco, what's your job, do you enjoy the forum ?
    Kind regards
    cool#9

  22. #22
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Hi expat
    So glad to meet a new french on RE forum ! Now we are two !!!
    Thanks for the word correction, i'll take english lessons in next september.
    I live near Monaco, what's your job, do you enjoy the forum ?
    Kind regards
    Yes, I think the forum is great and very helpful. Sorry to dissapoint though but I am actually an English expat.
    I was working on boats here in La Ciotat and you can see some of work in this thread
    http://www.refrigeration-engineer.co...e+wine+coolers
    now however I am an artisan. And you?
    Salutations.

  23. #23
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    Quote Originally Posted by expat View Post
    now however I am an artisan. And you?
    Salutations.
    Salut.
    I've my own (small) company doing after sales service, commissioning, maintenance contract...
    I work on VRF,VRV , split, multi ,packaged, chillers sometimes...
    See the pictures, some of my crazy situations !!
    rgds
    cool#9
    Last edited by cool#9; 09-10-2007 at 05:16 PM.

  24. #24
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: LG UB36NGB boring problem...

    When I have ain intermittent fuse blowing situation, I take a real farmers approach to fault finding...I put in th ebiggest fuse that I can fit, without causing a hazard to people...My thinking is that the cost of having me return 20 times, will be a lot more than quickly overloading and burning out the failing component.
    I know this is not a real high tech approach, but after running in and out for uncountable intermittent faults, I force myself to slow down, and create a situation that will finally identify the fault, once and for all.

Similar Threads

  1. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  2. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 02:48 PM
  3. what's the problem
    By botrous in forum Air Conditioning
    Replies: 35
    Last Post: 22-06-2008, 02:54 AM
  4. Hot start problem on VRV REYQ14M7W1B
    By cool#9 in forum Air Conditioning
    Replies: 9
    Last Post: 20-04-2007, 08:09 PM
  5. LG 10.5 kw cassette timer problem
    By Andy W in forum Air Conditioning
    Replies: 10
    Last Post: 25-06-2005, 07:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •