Meat display cases medium temp! R-22 Defrost settingS?
I need to know from anyone that can help? what should i set these three medium temp closed meat display cases for on time setting for defrost, its a regular paragon 8140 b type, for typical conventional defrost,,,
These cases are gravity fed, not forced air!
the other thing is, is theres a low pressure control to the compressor on the service factor tubing of a reciprocator, towards the top of the can type compressor, where the factory charges or checks the unit for pressure losses, etc; thats where some guy installed the compressor control , and i believe that its a problem to hook it up there it only short cycles the compressor during the off cycle, maybe its the valves leaking by, or its a solonid valve leaking, or finally its just not the right place to insatll a low pressure control to bring on the compressor!
am I right about this being a not a right place to install it?
this is a two question post!
I just have to get off my but after defrosting these and go and do the foot work , i guess!
I did find the defrost set at one time a day for 90 minutes! that didnt do the job!Last edited by isitfixedyet; 26-05-2007 at 06:47 AM. Reason: type-o's lol
-
26-05-2007, 07:58 PM #2
Re: Meat display cases medium temp! R-22 Defrost settingS?
These cases are gravity fed, not forced air!
Q2, you can fit a pressure switch anywhere. Try adjusting the diff.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
27-05-2007, 02:15 AM #3
Re: Meat display cases medium temp! R-22 Defrost settingS?
isitfixedyet, you win the prize for the most rambling question from the USA. Let's hope that you win out over the UK, once Refrigeration Idol is invented. But seriously
I need to know from anyone that can help? what should i set these three medium temp closed meat display cases for on time setting for Defrost, its a regular paragon 8140 b type, for typical conventional defrost,,,
These cases are gravity fed, not forced air!
the other thing is, is theres a low pressure Control to the Compressor on the service factor tubing of a reciprocator, towards the top of the can type Compressor, where the factory charges or checks the unit for pressure losses,
this is a two question post!
A two hour defrost once a day should be all you need. If you have your gauges on and the suction pressure fails to rise above the Saturated suction pressure of ice melting you likely have a leaking solenoid valve. This might also explain some of your other observations.
Similar Threads
-
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
finding a leak in 11 display cases all conected
By tsounos in forum Supermarket RefrigerationReplies: 52Last Post: 08-05-2007, 06:19 PM -
display case temp alarms
By shark26 in forum Supermarket RefrigerationReplies: 9Last Post: 17-01-2006, 10:07 AM -
George Barker Display Cases
By Mark in forum Supermarket RefrigerationReplies: 9Last Post: 02-09-2004, 10:43 PM -
Multiplex For Low Temp and Medium Temp
By allanbaker in forum Technical DiscussionsReplies: 0Last Post: 28-11-2002, 10:15 AM