    Hi
    I have to change the oil for a Kobe screw compressor its refrigerant is R22 and the oil type is Freol PU32N wich is not available in our market .what type of oil from Carrier or bitzer can replace it without problems
    Thank you in advance.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: refrigerant oil for screw compressor

    The number 32 looks like a 32cSt oil.
    SUNISO 3 GS or RENISO KM 32 or Emkarate RL 32H or Zerol 32 should do the job.

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    22

    Re: refrigerant oil for screw compressor

    Hello nabil you need ISO VISCOSITY GRADE 68 or above ester oil for screw compressors to run

  4. #4
    Join Date
    Mar 2005
    Location
    USA
    Age
    77
    Posts
    638
    Rep Power
    20

    Re: refrigerant oil for screw compressor

    You will do best to check the IOM for the unit and see what oil or alternate oils are approved by the vendor for use in the compressor. Most are using a semi-snythetic on R-22. For normal A/C duty, Iso 68 is the viscosity used for the screws. For lower or higher temps, they may require a different oil.

    Ken

  5. #5
    Join Date
    Dec 2006
    Location
    dd
    Posts
    5
    Rep Power
    0

    Re: refrigerant oil for screw compressor

    What's the te/tc?

  6. #6
    Join Date
    Mar 2005
    Location
    USA
    Age
    77
    Posts
    638
    Rep Power
    20

    Re: refrigerant oil for screw compressor

    te is evaporator temperature, I use ET
    tc is condensing temperature, I use CT

    Ken

  7. #7
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    20

    Re: refrigerant oil for screw compressor

    hello i maintain theses compressors on the same gas and the oil we have been using for the last 10 years is called zerico and its made by either mobil or esso i have never had any problems yet

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 01:39 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Refrigerant Compressor is Sweating
    By kaskiris in forum Trouble Shooting
    Replies: 10
    Last Post: 16-04-2007, 11:05 AM
  4. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 11:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •