    Arneg Alva Maxi Controls (switching off)



    Hello Everyone,
    Im new here and just wondering if anyone can help

    I have a store which is having the following installed:

    Alva Maxi 3.75metre and Alva Maxi 2.5metre running on one compressor.

    and a Alva Maxi 1.85 on 1 smaller compressor

    Now id like to turn these units off (to save power mainly) during the night and quite times.

    My supplier has told me that if i switch them off from the consumer unit on a daily basis, it would lead to me putting to much strain on the compressor (the unit outside), which inturn would reduce its life span. He has however told me that i can have digital temprature controls fitted which would allow me to reduce the temp(and save power) when i like.


    But surely there must be a way i can switch off the cabinets completely without damaging anything?



    Can anyone help?



  2. #2
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Arneg Alva Maxi Controls (switching off)

    k13shn

    Welcome to the forum, It might be worth seeking advice on energy saving from the contractor involved in the installation of the units, without compromising stock loss along the way.

    With Kind regards

    Mark

  3. #3
    k13shn's Avatar
    k13shn Guest

    Re: Arneg Alva Maxi Controls (switching off)

    Hi MarkFiddy, thanks for the reply.
    Ive spoken to the contractor and what i listen above was all he had to say really.

    Im just being doubtful though, because im sure on other makes of remote fridges the user has the option to turn them off....? But im being told theres not a way, and the only 'solution' being really to turn the temp down.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Arneg Alva Maxi Controls (switching off)

    Turning the power off at the consumer unit does not allow the system to 'close down' properly and will also disable compressor crankcase heaters and other safety equipment.

    Listen to your refrigeration specialist.
    Brian - Newton Abbot, Devon, UK