    icing up



    I have a walk in freezer that is freezing up a big block of ice at the tube sheet end where the TXV is. The coil and pan are clear of ice except for the one end. I am suspecting the defrost termination is comming out early and considering moving it present location closer towards the compressor on the suction line. Any ideas where else I might look?


    My wife says I don't listen to her....or something like that....

  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: icing up

    Hi,
    Try to change the defrost time. Make it longer.
    Also try to defrost more frequently.
    Cheers
    Even Einstein Asked Questions

  3. #3
    SteveRob's Avatar
    SteveRob Guest

    Re: icing up

    Quote Originally Posted by hvac01453 View Post
    I have a walk in freezer that is freezing up a big block of ice at the tube sheet end where the TXV is. The coil and pan are clear of ice except for the one end. I am suspecting the defrost termination is comming out early and considering moving it present location closer towards the compressor on the suction line. Any ideas where else I might look?
    Before, playing with the Def term, check that the ref system is working properly, de-Ice tube sheet and TEV with hot, water, blow lamp or a forced defost with the coil wrapped in carboard, as not to raise the room temp too high.

    Check out the TEV clean the orifce, check for oil cloging or blockage, reset the superheat, by calculating the spring lengthe or number of turns needed. then check with gauge and thermometer. But be sure also that the Condensing unit pack or Chiller is working correctly. Making mods should allways be last resort, be sure all aspects are correct to start with! before you take it on to re-design the system!

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: icing up

    I agree with SteveRob, check the coil gets full flooded and you don't have a massive superheat.

    Also check the heaters have not 'walked' out of place as this is a very common reason for icing up at one end.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  5. #5
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: icing up

    as above,make sure the heaters have not shifted to the other side of the coil just leaving the weather proof ends tight upto the coil block, if thats o/k i would move my termination probe or phail to the top coil run on the TEV side, set a 10 deg C, 20 min defrost, 5 min drip timer [thats very important] and watch it through its def cycle making sure the coil does not get too hot but gets enough heat in the problem area, as allready said,defrost first.

  6. #6
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: icing up

    Hi hvac01453

    you didn't say if the coldroom was getting to temperature ok.

    Regards
    Lrac

  7. #7
    Join Date
    Apr 2007
    Location
    new Zealand
    Posts
    8
    Rep Power
    0

    Re: icing up

    Just a thought. Is the coil being pumped out prior to the defrost or is the coil full of refrigerant? Also is the suction line piped for pumpdown or nonpumpdown. This does make a difference with defrosting.

    regads Steve

  8. #8
    Join Date
    Jan 2007
    Location
    australia
    Age
    46
    Posts
    49
    Rep Power
    0

    Re: icing up

    As above check the heater locations but also look for other factors... is the end of the evap that icing up located close to the door/entry....? if exscessive moisture is being drawn to the evap through worn door seals you will get excessive ice build up on end plate....and r they closing the door properly? I've found that most problems concerning ice up's can be customer related! Just a thought!

Similar Threads

  1. A/C icing back on suction
    By carlfoster in forum Trouble Shooting
    Replies: 23
    Last Post: 13-04-2010, 09:58 PM
  2. Krack Evaporator Icing
    By Rob@goldcoast in forum Technical Discussions
    Replies: 11
    Last Post: 15-08-2006, 02:53 AM
  3. TXV icing but room warming
    By liptow in forum Fundamentals
    Replies: 8
    Last Post: 30-06-2006, 09:01 AM
  4. What causes the icing of the evaporator
    By donrtc in forum Technical Discussions
    Replies: 12
    Last Post: 19-08-2005, 12:35 PM
  5. why icing on the suction valve
    By ong in forum Fundamentals
    Replies: 14
    Last Post: 12-06-2005, 10:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •