    Flooded Starts on Marine Air Conditioner



    I am having trouble with refrigerant (R-22) migration to the compressor on a CruiseAir system in a motor yacht. The unit has sea water cooling and a oil separator and capillary tube expansion. It would be difficult to add a pump-down solinoid. I understand that overcharging with refrigerant can contribute to this migration. My question is whether some degree of undercharging can prevent the migration. I have had to replace the hermetic compressor three times.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Flooded Starts on Marine Air Conditioner

    I don't think that one is an oil separator, but a liquid receiver. I think you need a suction accumulator and a suction riser (sort of pipe pointing upwards), or a suction filter with drainage.

    Last edited by NoNickName; 08-04-2007 at 10:39 AM.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Flooded Starts on Marine Air Conditioner

    Well,
    The obvious answer is to fit a crankcase heater, if the compressor is warmer than the rest of the system then there won't be any liquid in it when it starts.

    But as you are on a boat, the question arises, have you got the power supply to do it?

    Under charging?
    Well 2 negatives makes a positive but adding another fault? Will that really sort the first problem out?



    P.S
    As you said it was migration, I have assumed that it happens when the compressor stands, not when it is running?

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    Hi there,
    As Viking said "migration" is a term used for refrigerant movement when system is stopped. This is due to temp. difference.
    Flooding is a term used for liquid refrigerant reaching the compressor.
    The reasons :
    1- The hight difference between the evaporator and the compressor.
    2- If the system is off and the oil separator is in a cold place then the refrigerant gas inside could condense and through the floating valve enters the compressor.
    3-Malfunction of your expansion device.If there is cap tube then maybe you overcharged it.
    4-Any problem related to the evaporator that prevents good evaporation of the liquid refrigerant inside the evaporator. This can be verified by measuring the superheat. If it is near 0°C then this problem exists. Check these also, fan is working, frosting on the coil.
    Good luck.
    Cheers
    Even Einstein Asked Questions

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Flooded Starts on Marine Air Conditioner

    Why not fit a solenoid just before the capiliary. No need to pump down. That way you've only got the volume of refigerant that was in the evaporator and suction line instead of the condenser and liquid line to condense in the compressor.
    Is it migrating to the compressor from the evaporator, or leaking back from the highside?

    Jon

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    Hi,
    What monkey-spanners says is called "Minimum compressor protection". If there is a "flooded Start" then try it.

    What is the relative hight between the evaporator and the compressor?

    Cheers
    Even Einstein Asked Questions

  7. #7
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    The unit has an oil separator and a suction accumulator. The evaporator is two decks above the compressor and thirty feet forward. I think the refrigerant is migrating from the evaporator when the system is off, however I could fit a check valve downstream of the oil separator to prevent flow back from the condenser. The sequencing of a solenoid is difficult because of the electronic controls, and an interior crankcase heater is impossible on this hermetic compressor.

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Flooded Starts on Marine Air Conditioner

    Ahh,

    But the crankcase heater doesn't need to be internal, it's common practise to have external heaters strapped on to hermetic compressors.
    If it was me than I would strap one to the compressor and another one to the oil separator.
    (it would be cheap and easy to try)

  9. #9
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    The more I think about this, the more I think the refrigerant flooding is coming from the condenser back through the oil separator. The previous compressor failures were due to oil starvation and is why I added the oil separator. Due to space restrictions, I installed a Temprite 320 separator which does not use a float valve, but meters the oil back to the suction through a capillary tube. I think putting a check valve on the separator outlet will fix the problem. What do you think?

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flooded Starts on Marine Air Conditioner

    Surely a check valve in the oil separator outlet will defeat the object of the separator.

    It might be safer to simply put a solenoid valve in the line connected in with the compressor contactor.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    I don't mean the oil outlet from the separator, I mean the refrigerant outlet heading to the condenser.

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flooded Starts on Marine Air Conditioner

    OK, understood, but it will only stop the flow backwards towards the compressor discharge valves. If you are suspecting the compressor valves are letting by then that is the problem not the separator.

    However if you are returning the oil back to the compressor crankcase through a capillary line what is stopping the flow of refrigerant through the separator after the oil has returned?

    Also are there any oil traps in the system at all especially a loop by the evaporator to stop flow down through the yacht back to the compressor?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    I didn't mean to install the check valve on the oil outlet from the separator, but on the refrigerant line from the separator to the condenser.

  14. #14
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Nothing can stop the refrigerant flow through the cap tube after the oil, but when the compressor is running, this is not a problem. However, when the compressor stops, the only refrigerant return through the tube would be that which is trapped between the check valve and the discharge valves.

  15. #15
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    There are no oil traps between the evaporator and the compressor, but there are no vertical risers with upward flow. It has a steady downward slope all of the way.

  16. #16
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flooded Starts on Marine Air Conditioner

    Quote Originally Posted by Mayball View Post
    Nothing can stop the refrigerant flow through the cap tube after the oil, but when the compressor is running, this is not a problem. However, when the compressor stops, the only refrigerant return through the tube would be that which is trapped between the check valve and the discharge valves.
    True, sorry I wasn't thinking straight
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  17. #17
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    Hi Mayball,

    Try an inverted trap before the condenser to prevent liquid refrigerant going into the compressor. Also install the check valve after the oil separator (on the refrigerant line), as mentioned before.
    Good luck.
    Even Einstein Asked Questions

  18. #18
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Smile Re: Flooded Starts on Marine Air Conditioner

    Hi Lana

    Because this installation is also a heat pump, the oil separator discharges through a reversing valve which, in effect, has both an oil trap and an inverted oil trap that the refrigerant must go through when traveling backwards from the condenser to the oil separator, so I think that part is covered.

    Mayball

  19. #19
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flooded Starts on Marine Air Conditioner

    Reading back though this thread and it seems that the installation of the oil separator is the cause of the floodback problems as you suspect.

    I will therefore stick with my previous suggestion:- fit a solenoid valve into the oil line from the separator that will shut down when the compressor is idle.

    It can be fed via a relay which is triggered by the power line to the compressor.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  20. #20
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Certainly, the solinoid on the oil line will eliminate any chance of refrigerant migration to the suction side, and there is already a spare reley to drive it, that used to be used on a DC cooling water pump. The question in my mind is which is more reliable (least chance of failure): the electro/mechanical solinoid-relay combination, or a mechanical check valve in the hot discharge gas environment coming from the oil separator.

    Thanks for your input, Brian

    Mayball

  21. #21
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flooded Starts on Marine Air Conditioner

    A check valve will impart some form of restriction in the refrigerant line but obviously has its merits.

    The modern solenoid is a pretty reliable item nowadays and using one with a 'timed cycle' is one of the Temprite options with the 320 separator.

    I have got a little confused as to where the oil return capillary is connected to but if it is connected into the suction to the accummulator then it would give you another 'reservior' for any refrigerant that gets through.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  22. #22
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Brian

    I did have the oil return line connected to the process tube on the suction of the compressor. There is no room for a suction accumulator on the condensing unit. Cruisaire did have what looks like a 2" D copper strainer on the suction line before the compressor, but when I took it off, you could see right through it, so I think it was only a muffler. I replaced it with a suction filter/dryer, since that was all the space I had. The filter/dryer has inlet and outlet pressure taps, and I could attach the oil line to the inlet tap, if that seems appropriate.

    Don

  23. #23
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Flooded Starts on Marine Air Conditioner

    Sorry Don, you said that you had an accumulator in an earlier post that's why I suggested that route.

    I am surprised that being a heat pump the unit does not have an accumulator as on changeover there is always the risk of liquid going straight into the compressor, especially on defrost, however....

    Yes, why not connect onto the filter/drier.

    My admiration of you doing this work on board at your respectable age is growing Don, keep it up
    Last edited by Brian_UK; 09-04-2007 at 11:43 PM. Reason: Spelling, as usual!
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  24. #24
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Brian,

    The only reason I keep working here is it is 80 Degrees here in Puerto Vallarta. By the way, how is the weather there in Dorset?

    Don

  25. #25
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    Hi Don,

    I suggest that you draw a simple schematic of your system and attach it here. This would clear so many questions and help to find a solution ASAP.
    Cheers
    Even Einstein Asked Questions

  26. #26
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Flooded Starts on Marine Air Conditioner

    You mentioned that there is a steady downward slope in the suction line, from the evaporator to the compressor. It is entirely possible (and not uncommon) that liquid refrigerant gathers in the evaporator (coldest point) during the off cycle and is then delivered by gravity (as opposed to migration) to the compressor inlet. This can be eliminated/minimized by looping the suction line above the evaporator and then down to the compressor, thus trapping the liquid in the evaporator.
    Last edited by Gary; 10-04-2007 at 06:34 AM.

  27. #27
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Lana,

    In the attachment, the following legend applies:

    SA - Compressor, BC - Oil Separator, DE - Proposed Check Valve, FG - Reversing Valve, H - Solenoid Valve Proposed by Brian UK, IJ - Water Cooled Condenser, KL - Liquid Line Filter/Dryer, MN - Cap Tube, OP - Evaporator, QR - Suction Filter/Dryer. The condenser is actually coaxial and is located above the compressor.

    Mayball
    Attached Images Attached Images

  28. #28
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Gary,

    The suction line does leave the evaporator at an elevation above the evaporator. This fact, and the fact that the migration did not happen until I added the oil separator, leads me to believe that the migration is not coming from the evaporator.

    Thanks
    Mayball

  29. #29
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    Hi MAyball,

    In the diagram the reversing valve is not right. It must be connected to both heat exchangers. Can you correct it and show the actual one? Also where is the accumulator?
    The suction line must be connected to the reversing valve also.
    Lana
    Last edited by lana; 10-04-2007 at 12:19 PM.
    Even Einstein Asked Questions

  30. #30
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Flooded Starts on Marine Air Conditioner

    I am concerned that an oil separator was added without resolving the original oil return problem. There should be a trap at the evaporator outlet.

    Is there an oil sightglass on the compressor?

    What makes you believe the compressor is flooded on startup?

    Is it possible that the compressor is flooding with excess oil rather than refrigerant?

  31. #31
    Join Date
    Mar 2007
    Location
    england
    Posts
    1
    Rep Power
    0

    Re: Flooded Starts on Marine Air Conditioner

    hi sounds like you have a flooding back problem rather than migration. Is there sufficient air flow across the evaporator/ evaporator fan running?
    I have installed/worked on many of these systems some times the boat manufactures do not allow for air return or squash the air outlet hose considerably restricting flow. Is the fan fuse ok?? hope this helps.

  32. #32
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Gary,

    The oil separator was installed to resolve the oil return problem. The previous two compressor failures were due to oil starvation. I believe the oil was trapped in the evaporator. I measured the oil in the compressors that failed. The first two were about 1/3 low with dirty oil. The last one was almost exactly right with clean oil. However, when I depressured that last compressor to check the oil, a very large amount of refrigerant boiled off. There is no sight glass on this Tecumseh 1 HP compressor. That last compressor failed after the longest shutdown period in its service; previous shut downs were normal cycling.
    mayball

  33. #33
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Lana

    I only showed the high side part of the reversing valve because that is the part that is involved in my problem. The suction line is also connected to the reversing valve, but since I am not a great artist, I left that part out. I misspoke when I said there was an accumulator, only the suction filter/dryer, which I installed as there is no room for an accumulator. The original condensing unit had only a muffler.

    Mayball

  34. #34
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi HFC134a,

    There is plenty of air flow through the evaporator. In fact it has twice the fans of an identical unit on the same boat, that is running fine. The evaporator is sandwiched between inlet and outlet plenums and use grills from and to the air conditioned space rather than hose ducts.

    Mayball

  35. #35
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    Quote Originally Posted by Mayball View Post
    I misspoke when I said there was an accumulator, only the suction filter/dryer, which I installed as there is no room for an accumulator. The original condensing unit had only a muffler.
    Hi Mayball,

    I think your problem is 100% for not having an accumulator. In a heat pump unit, an accumulator is a must.
    When changing the mode (cooling & heating) there is definitely liquid flood back to the compressor.
    I suggest that you make some room to put an accumulator.
    Good Luck.
    Even Einstein Asked Questions

  36. #36
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Lana,

    I totally agree that this is a poor design, but this is Cruisair's design. Also, this unit has never been run as a heat pump and the reversing valve has never been exercised. Further, it probably never will be used as a heat pump, because the cabin has a very adequate diesel heater and the owner said he would never use the heat pump. I will, however, caution him on its use, and, if he wishes will disable the reversing valve.

    Mayball

  37. #37
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    Hi,

    I think after 36 posts we still don't understand the actual problem .

    Please answer the following questions very carefully and clearly.

    1- Is there only one compressor on the unit or you have two parallel one?
    2- Is there an accumulator?
    3- Is this a heat pump or not? If this is not going to be used as a heat pump then take away any unnecessary parts like the reversing valve and make the system simpler to handle.

    Cheers
    Even Einstein Asked Questions

  38. #38
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Lana,

    Sorry I seem so vague.
    1. There is only one compressor on the unit. There is, however another system on the boat identical to this one.
    2. There is no accumulator.
    3. This is an air conditioner that can function as a heat pump. This condensing unit/heat pump was ordered by the customer and he hired me to install it and connect it to his existing air handler (replacing an existing 134a Glacier Bay feed to that air handler). I cannot remove the reversing valve because the customer wants the capability available when he sells the boat.

    Mayball

  39. #39
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Flooded Starts on Marine Air Conditioner

    What was the fault with the three compressors? Valves broken? Burnt windings? Other?

  40. #40
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Flooded Starts on Marine Air Conditioner

    Quote Originally Posted by Mayball View Post
    There is, however another system on the boat identical to this one.
    Not really. It sounds like this one has twice the airflow. Does it also have twice the evaporator? Perhaps twice the refrigerant charge?

  41. #41
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Gary,

    I only opened one of the failed compressors: one of the two that were oil starved. It had wiped the main bearing and the connecting rod bearing. The third compressor which had not lost oil and, I believe, failed due to a flooded start had close to a dead short in the windin(s). On energing the compressor, it drew 67 amps and tripped the breaker. Its valves appeared to be OK.

    The second system is identical to the failed system except it has one fan instead of two and and the failed system has about double the distance and elevation between the condensing unit and the air handler. It therefore has a larger refrigerant charge, having twice the length of liquid line.

    Mayball

  42. #42
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Flooded Starts on Marine Air Conditioner

    During the off cycle, given an open path between the high side and the low side, most of the refrigerant charge will migrate to, and condense in, the coldest part of the system. The larger the charge, the more refrigerant to migrate.

    The purpose of the liquid line solenoid is to close the path between high side and low side, and the purpose of the crankcase heater is to ensure that the compressor is never the coldest part of the system.

    You need to install a liquid line solenoid, the closer to the cap tube the better, which closes when the compressor stops... and you need a crankcase heater.
    Last edited by Gary; 11-04-2007 at 01:06 PM.

  43. #43
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Gary,

    I agree with you on the advantages of a crankcase heater but I disagree on the need for a solenoid at the entrance to the evaporator cap-tube. In fact, that solenoid would exacerbate the problem. Consider the following:
    1. There was no problem with refrigerant migration or flooded starts, until I added the oil separator to solve the oil starvation problem.
    2. The addition of the oil separator to the compressor discharge does not affect the suction line or cause refrigerant migration down the suction line to the compressor when the unit is shut down.
    3. The addition of a solenoid before the evaporator would eliminate the off cycle equalization of pressure through the capillary tube, leading to harder starts, and worse, would trap the liquid between the condenser and the solenoid. This liquid would then move backwards through the condenser to the oil separator and thence out the oil outlet of the separator to the compressor suction, driven, not by temperature difference, but by pressure difference.

    This is why both Brian UK and I see an advantage of placing the solenoid on the oil line between the separator and the compressor suction. To my mind, however, a more simple solution is a check valve added to the line between the oil separator and the condenser. Both the solenoid and the check valve would stop any backward movement of refrigerant from the condenser to the compressor suction. This is, of course, not a problem when there is no separator because back flow is prevented by the compressor valves.

    Mayball
    Last edited by Mayball; 11-04-2007 at 07:20 PM.

  44. #44
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    3. The addition of a solenoid before the evaporator would eliminate the off cycle equalization of pressure through the capillary tube, leading to harder starts, and worse, would trap the liquid between the condenser and the solenoid. This liquid would then move backwards through the condenser to the oil separator and thence out the oil outlet of the separator to the compressor suction, driven, not by temperature difference, but by pressure difference.
    In my opinion this is completely wrong.

    This is why both Brian UK and I see an advantage of placing the solenoid on the oil line between the separator and the compressor suction. To my mind, however, a more simple solution is a check valve added to the line between the oil separator and the condenser. Both the solenoid and the check valve would stop any backward movement of refrigerant from the condenser to the compressor suction. This is, of course, not a problem when there is no separator because back flow is prevented by the compressor valves.
    Do that.

    Also do whatever Gary said in his last post.

    Cheers
    Even Einstein Asked Questions

  45. #45
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Flooded Starts on Marine Air Conditioner

    Quote Originally Posted by Mayball View Post
    1. There was no problem with refrigerant migration or flooded starts, until I added the oil separator to solve the oil starvation problem.
    On the contrary, I believe the oil was washed out of the first two compressors by flooded starts from migration.

    Quote Originally Posted by Mayball View Post
    2. The addition of the oil separator to the compressor discharge does not affect the suction line or cause refrigerant migration down the suction line to the compressor when the unit is shut down.
    Migration to the separator does not affect the suction line. Rather it dumps liquid directly into the compressor via the oil return line. Oil separators (particularly those mounted below the condenser) are a target for migration from the condenser. That's why the check valve after the separator is a very good idea.

    Quote Originally Posted by Mayball View Post
    3. The addition of a solenoid before the evaporator would eliminate the off cycle equalization of pressure through the capillary tube, leading to harder starts, and worse, would trap the liquid between the condenser and the solenoid. This liquid would then move backwards through the condenser to the oil separator and thence out the oil outlet of the separator to the compressor suction, driven, not by temperature difference, but by pressure difference.
    It doesn't work that way.

    Quote Originally Posted by Mayball View Post
    This is why both Brian UK and I see an advantage of placing the solenoid on the oil line between the separator and the compressor suction. To my mind, however, a more simple solution is a check valve added to the line between the oil separator and the condenser. Both the solenoid and the check valve would stop any backward movement of refrigerant from the condenser to the compressor suction. This is, of course, not a problem when there is no separator because back flow is prevented by the compressor valves.
    Congratulations. You now have two migration targets.
    Last edited by Gary; 11-04-2007 at 11:23 PM.

  46. #46
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Lana,
    Are you saying that everything I said in item 3 is wrong? Are you saying that it could not happen that way? If so, could you be more specific in explaining why?
    Mayball

  47. #47
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    Hi Mayball,

    Gary Said it all.

    The addition of a solenoid before the evaporator would eliminate the off cycle equalization of pressure through the capillary tube, leading to harder starts,
    Why would be a hard start? This is the whole point of Pump-Down.

    and worse, would trap the liquid between the condenser and the solenoid. This liquid would then move backwards through the condenser to the oil separator and thence out the oil outlet of the separator to the compressor suction, driven, not by temperature difference, but by pressure difference.


    If every piping and trap is installed correctly then why would the liquid move? You say it moves because of pressure difference . Difference between what points? I guess you mean between compressor crankcase pressure and pressure in the condenser. BUT there is the valve reeds there. Of course if we leave a system in pump-down for a very long time this might happen but for start and stop this will not. Believe me.

    Installing a solenoid valve and implementing pump-down is the best way to protect the compressor from liquid refrigerant during off cycle. If you want read the Copeland manual (the 5 volume).

    Hope this clear some points
    Good Luck
    Cheers
    Even Einstein Asked Questions

  48. #48
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Gary,

    If 2/3 of the oil in the system washed out during flooded starts, why has none of it ever come back? Of course, 1/3 of the oil did leave each of the two compressors, and didn't come back, but I think it resides in the evaporator. If it blew through the compressor on flooded starts it would seem more likely to return, since it is passing through the system in slugs, sort of like the oil trap effect. It seems to me more likely that the oil passed into the system, in the normal fashion (the unit ran 24/7 all summer last year in the tropics before it failed) and is still in the evaporator and it isn't coming back. I can't imagine it lasting very long with a flooded start each time it cycled.

    Mayball

  49. #49
    Join Date
    Dec 2004
    Location
    Mexico
    Age
    86
    Posts
    58
    Rep Power
    20

    Re: Flooded Starts on Marine Air Conditioner

    Hi Lana,
    The pump down protects the system on the suction side, but it does this by pumping into the high side. If it can then move from the high side to the low side by pressure differential through the oil separator, then the flooded start possibility is aggrevated. That is why I thought it would be better to install the check valve before the condenser. I still think the flooded start came from the condenser refrigerant moving backward through the oil separater rather than from the evaporator moving forward.

    Mayball

  50. #50
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Flooded Starts on Marine Air Conditioner

    The pump down protects the system on the suction side, but it does this by pumping into the high side. If it can then move from the high side to the low side by pressure differential through the oil separator, then the flooded start possibility is aggrevated
    .

    As we said before, if the oil separator body gets colder then refrigerant gas would condense in the oil separator and goes into the crankcase. This is why we suggested to install an inverted trap and check valve on the discharge line.
    If there is no liquid refrigerant in the oil separator then it can not move to the compressor.

    You agree with us on the solution but you don't agree with the reason .

    Cheers
    Even Einstein Asked Questions