    Sanyo



    I require help with a series of Sanyo Heat Pumps on R407C
    Installed around 5 years ago.

    Indoor Units are Ceiling Concealed Type and ducted to areas within space

    Each outdoor unit is in the region 14Kw ( Approximate guess)

    There are 5 outdoor units linked to 5 Indoor

    Only 2 Controllers, I have been told 1 controller linked to 3 systems and 1 controller linked to 2 systems.

    In heat mode both controllers display Error Code P4 simultaneously

    Will appreciate some feedback



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Sanyo

    Abe, try this Sanyo site...

    http://www.sanyo.com/industrial/HVAC...productID=1284

    I don't know if it is the correct model but you can download technical manual, about 11mb and other docs.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2004
    Location
    england
    Age
    59
    Posts
    5
    Rep Power
    0

    Re: Sanyo

    All p codes are for protective devices - but i cant remember which one P04 is. But its to go with the outdoor maybe a pressure switch.

    can find out on monday for you

    Best regards

  4. #4
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Sanyo

    P4 = High pressure switch is activated.
    Check your refrigerant pressure, condenser fan and condenser coil cleaniness.

  5. #5
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Sanyo

    Quote Originally Posted by s19652 View Post
    All p codes are for protective devices - but i cant remember which one P04 is. But its to go with the outdoor maybe a pressure switch.

    can find out on monday for you

    Best regards


    Thank you, much appreciated

  6. #6
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Sanyo

    Quote Originally Posted by Cofreth View Post
    P4 = High pressure switch is activated.
    Check your refrigerant pressure, condenser fan and condenser coil cleaniness.

    The outdoor units were slung high up on a wall , and I could not get up to take readings, also was raining.

    I started in cooling mode and from a visual point i saw all the fans were operating.

    I then switched to Heat mode and thats when both controllers displayed P4

    Using two controllers makes it more difficult which outdoor unit is at fault. I think the installer has daisy chained.

    3 Outdoors on one controller, two on the other, however both controllers displayed P4 at same time.

  7. #7
    Join Date
    Apr 2006
    Location
    Essex
    Age
    55
    Posts
    21
    Rep Power
    0

    Re: Sanyo

    From past experience ive always found oceanair very good in helping me out on sanyo splits - didnt realise just how deep you can go via the controllers into the operation of these units. I had something similar 6 months back which was
    eventually traced to a dodgy discharge sensor which would initially run the fans at 100% then over the space of 4-5 minutes would drop them down to 0% Helpful!

  8. #8
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Sanyo

    Hi Abe,

    Following info from Sanyo Tech man

    Symptom: LCD on the remote controller displays “CHECK P04”. (High-pressure
    switch activation warning)

    If the system operates again:
    High-pressure switch activation

    (Both cooling and heating)
    • Electronic refrigerant control valve
    defect
    • Refrigerant over-charged
    (Cooling)
    • Outdoor unit, heat exchanger dirty,
    clogged
    • Outdoor unit air short
    • Outdoor fan stopped
    (Heating)
    • Outdoor unit air short
    • Indoor unit, heat exchanger dirty,
    clogged
    • Large pipe side service valve
    closed
    • Indoor fan stop
    • Air filter clogged


    If the system does not operate again:
    Are there connection defects in the wiring?
    NO = HP switch defect, YES= Repair wiring!

  9. #9
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Sanyo

    Abe

    If you PM me I'll email a pdf that has info....to big to attach here.

    Adrian

  10. #10
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Sanyo

    Abe,
    Got PM,
    Email sent with pdf.

    Adrian.