    Question power factor



    W ondering if anybody can help, I have a 50 hp motor running a belt driven compressor. FLA is 47.1A at 575v 60hz. SF of 1.25 and a efficiency of 75%.
    could anyone tell me how to figure out the watts used at full load conditions. Ultimately I would like to figure out the power factor for the whole plant. If anyone can shed some light on this it would be much appreciated.
    thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: power factor

    Ho Goodguy, not my area really but doing a Google on power factors brings up a fair selection...

    Here's one to start with......
    http://www.angelfire.com/pa/baconbacon/page2.html
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: power factor

    Unless you know the RMS drawn current, you are unable to know the power factor. Supposing the FLA is the actual running current:
    50hp = 36.75kW
    36.75/47.1/1.73 = 0.451 - very bad power factor.

  4. #4
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: power factor

    Hi Goodguy,

    The only way of measuring the power factor is with a proper KVA power meter (as opposed to an electricity meter which will only register kWh). You will need to measure both current and voltage.
    A power meter should actually give you a direct reading of the power factor. If you are considering the whole site then it would be worth renting one in or possibly purchasing one?

    Motors can have a power factor anywhere between 0.1 up to 0.9 depending upon the loading. Lightly loaded motors having a poor power factor.

    I guess the figures you quote are purely those from the motor rating plate.

    A motor is normally rated at a pf of 0.8 lagging, thus in your case:

    50 hp = 50 x 746 = 37.300 kW ( = P) [1 hp = 746 W]

    P= E x I x 1.732 x pf
    = 575 x 47.1 x 1.732 x pf
    = 46.907 x pf (kW)
    thus
    pf = 37.300 / 46.907
    = 0.795

    I expect that your actual p.f will be 0.4 to 0.7 as generally when designing, the 'safety factors' push the motor rating up to the next standard size motor, so in reality your motor will not be fully loaded, and hence will not be at its most efficient loading.

    Have you investigated VF Drives, as these can vastly improve efficiency and reduce losses.
    Energy useage these days is a 'hot topic'.

    try looking at www.carbontrust.co.uk
    and search for 'motors' GPG002 is intresting.
    Hope this helps.

    ECM.

  5. #5
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: power factor

    Thank you all for your knowledge and web links. But one further question, at what point do you start taking corrective actions fo poor power factor?

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: power factor

    Quote Originally Posted by Electrocoolman View Post
    Hi Goodguy,

    The only way of measuring the power factor is with a proper KVA power meter (as opposed to an electricity meter which will only register kWh). You will need to measure both current and voltage.
    A power meter should actually give you a direct reading of the power factor. If you are considering the whole site then it would be worth renting one in or possibly purchasing one?

    Motors can have a power factor anywhere between 0.1 up to 0.9 depending upon the loading. Lightly loaded motors having a poor power factor.

    I guess the figures you quote are purely those from the motor rating plate.

    A motor is normally rated at a pf of 0.8 lagging, thus in your case:

    50 hp = 50 x 746 = 37.300 kW ( = P) [1 hp = 746 W]

    P= E x I x 1.732 x pf
    = 575 x 47.1 x 1.732 x pf
    = 46.907 x pf (kW)
    thus
    pf = 37.300 / 46.907
    = 0.795

    I expect that your actual p.f will be 0.4 to 0.7 as generally when designing, the 'safety factors' push the motor rating up to the next standard size motor, so in reality your motor will not be fully loaded, and hence will not be at its most efficient loading.

    Have you investigated VF Drives, as these can vastly improve efficiency and reduce losses.
    Energy useage these days is a 'hot topic'.

    try looking at www.carbontrust.co.uk
    and search for 'motors' GPG002 is intresting.
    Hope this helps.

    ECM.
    Electrocoolman, nice explanation.
    Power factor could also be increased with an automatic switching capacity battery.
    I thought the net voltage was 600 V in Canada?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: power factor

    peter1, your right, net voltage is closer to 600v and have seen it around 620v in normal circumstances.
    It seems thought, alot of nameplates are only listed 575v, in my experience anyway. Is this common?

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: power factor

    Quote Originally Posted by Electrocoolman View Post
    try looking at www.carbontrust.co.uk
    and search for 'motors' GPG002 is intresting.
    .
    This link is easier http://www.carbontrust.co.uk/Publica...&metaNoCache=1
    Do also once a search on refrigeration on this website
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Oct 2001
    Location
    New Jersey
    Age
    71
    Posts
    83
    Rep Power
    0

    Re: power factor

    Quote Originally Posted by goodguy View Post
    Thank you all for your knowledge and web links. But one further question, at what point do you start taking corrective actions fo poor power factor?
    Well, if it gets too low I'm sure the power company would let you know. We had capacitors installed in our plant many years ago because of a low power factor. I know now we have a meter where power comes in and tells you what the power factor is. The lower the power factor the cheaper power is for you. Inductive reactance (motors) are responsible for this.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: power factor

    I can speak for Belgium: <0.92
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •