    Wiring Fault



    Hi all

    I was looking at a newly installed island of freezers today and noticed one case with the Live and Neutral reversed.I rectifed this fault straight away however what long term effect would this have if left faulty.

    Kind Regards

    Bernard



  2. #2
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Wiring Fault

    Bernard,
    As you discovered, in normal operation it would still run, however in a fault condition it could have caused a fire, depending upon the type of protection on the supply circuit.
    If it was only Single pole switching on the unit, the unit would still have a live supply to it when switched off.
    Fuse protection is again wired in the supply live, so under a fault condition to earth the unit would have no protection...
    ....and what about the unsuspecting service tech who doesnt bother to check before diving in?

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Wiring Fault

    Once fitted a dairy deck and AC in a corner shop and found on commissioning that the live and neutral into the mains board where reversed Shop owner didn't seem too bothered, he'd had a mate do the electrics cheep

    Cheers Jon

  4. #4
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Wiring Fault

    Quote Originally Posted by Electrocoolman View Post
    Bernard,
    As you discovered, in normal operation it would still run, however in a fault condition it could have caused a fire, depending upon the type of protection on the supply circuit.
    If it was only Single pole switching on the unit, the unit would still have a live supply to it when switched off.
    Fuse protection is again wired in the supply live, so under a fault condition to earth the unit would have no protection...
    ....and what about the unsuspecting service tech who doesnt bother to check before diving in?
    This may be the case but what about all of this italian kit coming into the country that neutral switches on all of the controls.

    Regards
    Lrac

  5. #5
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Wiring Fault

    Hi Lrac,
    The 'fuse' protection would still be in the live supply feed despite controls switching the neutral.

    The other scenario I have come across is equipment wired to USA standards but misconnected in UK. USA colour codes is 'Black = Phase' 'White = Neutral'
    Black sometimes ends up being wired to Neutral.
    Just remember Black Death!

  6. #6
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: Wiring Fault

    Trust me, we get confused when we have your equipment over here. I had to convert a very complicated machine (not refrigeration) from your standards to ours, in order to satisfy our local inspectors. Some inspectors will let us placard the machines, others will demand new color IDs on the ends. Some will want rewiring.
    One customer imported a dehumidifier from Japan. He was forced to replace all the components in the electrical panel.

  7. #7
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Wiring Fault

    Hi NH3LVR,
    On your two pin mains plugs is it the WIDE prong that is the phase?

  8. #8
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: Wiring Fault

    Quote Originally Posted by Electrocoolman View Post
    Hi NH3LVR,
    On your two pin mains plugs is it the WIDE prong that is the phase?
    If memory serves the narrow one is the hot (to ground, or earth) one.
    Let me check.
    If the hotel is wired correctly, that is the way it is.
    If it is not wired correctly I may not survive my shower and it has been nice knowing you all.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Wiring Fault

    Quote Originally Posted by NH3LVR
    If it is not wired correctly I may not survive my shower and it has been nice knowing you all.
    Now you be careful with this. It would be shame to loose a good tech because of this.
    If all else fails, ask for help.


  10. #10
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: Wiring Fault

    Quote Originally Posted by US Iceman View Post
    Now you be careful with this. It would be shame to loose a good tech because of this.
    Well I survived and will continue to spread my sense of humor and good cheer.
    Now if I can ever finish this decommisioning, I can go home and work on the job 15 minutes from the shop!