    Fujitsu Problem



    I installed a Fujitsu a 12RQ unit a few months ago for my den. The room is about 325 sq ft. The unit will run until desired temp is reached and cycle off. The unit will then cycle on and off continually about every 4 or 5 minutes. Is the unit oversized or is there a problem with the unit?



  2. #2
    Join Date
    Dec 2006
    Location
    London
    Posts
    32
    Rep Power
    0

    Re: Fujitsu Problem

    when you say it cycles every 4-5 minutes do you mean that it comes on after 5 mins, runs for a minute or so, goes off and then comes on again after another 5 mins. if that it the case it sounds normal. if on the other hand it constantly comes on and goes off within the space of a minute then that could indicate a problem

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Fujitsu Problem

    Dehum mode???

  4. #4
    Join Date
    Dec 2006
    Location
    lost
    Age
    52
    Posts
    7
    Rep Power
    0

    Re: Fujitsu Problem

    You give very very limited info but.......perhaps the problem may be more due to undersize not oversize.
    You say it's in your Den.
    A 325sq ft den, containing PC, maybe a lazer printer good lighting and a large south facing window, aga in the kitchen downstairs??????

    Freezing up anyone??

    More info needed me thinks..

    regards

  5. #5
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: Fujitsu Problem

    Quote Originally Posted by a1onetimeagain View Post
    may be more due to undersize not oversize.
    Does the system maintain the desired room temperature easily, with it's frequent/short on periods? ie, If hardly any load, maybe the thing does not need to operate; if it struggles to maintain the room temp - that's the other side of the coin.

  6. #6
    Join Date
    Feb 2007
    Location
    Spain
    Age
    45
    Posts
    26
    Rep Power
    0

    Re: Fujitsu Problem

    My be the unit is short circling. Air flow bouncing of something to close, air flow reentering the unit giving false temp, unit thinking it's got the room to its desired temp?

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Fujitsu Problem

    Quote Originally Posted by tennern View Post
    The unit will then cycle on and off continually about every 4 or 5 minutes.
    How long is it on?

    How long is it off?

  8. #8
    Join Date
    Feb 2007
    Location
    modesto
    Posts
    7
    Rep Power
    0

    Re: Fujitsu Problem

    Quote Originally Posted by Gary View Post
    How long is it on?

    How long is it off?
    On for 3 minutes...off for 4 minutes,no matter what temperature setting

  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Fujitsu Problem

    Quote Originally Posted by tennern View Post
    On for 3 minutes...off for 4 minutes,no matter what temperature setting
    Sounds like Dehum mode.......

  10. #10
    Join Date
    Feb 2007
    Location
    modesto
    Posts
    7
    Rep Power
    0

    Re: Fujitsu Problem

    Quote Originally Posted by The Viking View Post
    Sounds like Dehum mode.......
    not running in dry mode

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Fujitsu Problem

    Hi Guys

    if it was a fridge I would say it is either over sized or the control (return air) sensor is picking up on air short cycling straight back to the return air grill form the discharge grill. Is the indoor unit free to circulate the air around the room.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  12. #12
    Join Date
    Feb 2007
    Location
    modesto
    Posts
    7
    Rep Power
    0

    Re: Fujitsu Problem

    Quote Originally Posted by Andy View Post
    Hi Guys

    if it was a fridge I would say it is either over sized or the control (return air) sensor is picking up on air short cycling straight back to the return air grill form the discharge grill. Is the indoor unit free to circulate the air around the room.

    Kind Regards Andy
    yes,the indoor unit is free to circulate air

  13. #13
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Fujitsu Problem

    Quote Originally Posted by tennern View Post
    yes,the indoor unit is free to circulate air

    Hi

    then is it possibly over sized

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  14. #14
    Join Date
    Feb 2007
    Location
    modesto
    Posts
    7
    Rep Power
    0

    Re: Fujitsu Problem

    Quote Originally Posted by Andy View Post
    Hi

    then is it possibly over sized

    Kind Regards Andy
    with everything else eliminated then oversized must be the case....i guess the unit will short cycle itself to an early grave

  15. #15
    Join Date
    May 2006
    Location
    china
    Posts
    98
    Rep Power
    18

    Re: Fujitsu Problem

    whether the refrigeratory has the refrigerating duty or it's a empty room? If it's vacancy, there's not a problem.

  16. #16
    Join Date
    Feb 2007
    Location
    modesto
    Posts
    7
    Rep Power
    0

    Re: Fujitsu Problem

    Quote Originally Posted by ernestlin View Post
    whether the refrigeratory has the refrigerating duty or it's a empty room? If it's vacancy, there's not a problem.
    i don't quite understand your answer...can you please elaborate

  17. #17
    Join Date
    May 2006
    Location
    china
    Posts
    98
    Rep Power
    18

    Re: Fujitsu Problem

    My speaking is if there's normal refrigeration duty when the compressor unit is working? Just as above mentioned points, if your compressor is over sized? If it is, the pull down time is too short results in the frequent ON-OFF action. But, if your fridge is empty when you run the refrigerated unit, the reason is the insufficient refrigeration duty, not the compressor.

  18. #18
    Join Date
    Mar 2007
    Location
    Sheffield
    Age
    45
    Posts
    8
    Rep Power
    0

    Re: Fujitsu Problem

    Sounds to me like the compressor is running fine to start with but then is overheating and the short cycling is being caused by the compressors internal overload - as the compressor cools the overload resets and the compressor runs again until the overload trips again. If this is the case then there is a major problem. Check these:

    1. Condensor fan operation
    2. Refrigerant charge - abnormal charge will cause abnormally high compressor temps
    3. Available air flow to condensor.

    Hope this helps

  19. #19
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fujitsu Problem

    Quote Originally Posted by Si@airconworld View Post
    Sounds to me like the compressor is running fine to start with but then is overheating and the short cycling is being caused by the compressors internal overload - as the compressor cools the overload resets and the compressor runs again until the overload trips again. If this is the case then there is a major problem. Check these:

    1. Condensor fan operation
    2. Refrigerant charge - abnormal charge will cause abnormally high compressor temps
    3. Available air flow to condensor.

    Hope this helps
    I don't think so, this size of compressor would need several hours to reset after an overheat.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  20. #20
    Join Date
    Mar 2002
    Location
    Sydney Australia :D
    Age
    53
    Posts
    47
    Rep Power
    0

    Re: Fujitsu Problem

    Sounds to me like the unit has reached set point and is cycling on & off normally. Is the fan on automatic this will cause the fan to start & stop.
    :cool: Do the job once & do it right. :cool:

  21. #21
    Join Date
    Feb 2007
    Location
    Australia
    Age
    70
    Posts
    15
    Rep Power
    0

    Re: Fujitsu Problem

    What is the temperature of the air entering the front grille near the sensor?
    Is the sensor in the correct location (not touching a cold coil).
    Is the remote operating correctly? Such as changing fan speed, louvres etc.

  22. #22
    Join Date
    Apr 2007
    Location
    newcastle
    Posts
    11
    Rep Power
    0

    Smile Re: Fujitsu Problem

    i had this problem before with fujitsu .take out the return air probe and place it as far away from the unit as you can at ceiling height rejoin the cables by crimping .just use bell wire .and away it should go

  23. #23
    Join Date
    Feb 2007
    Location
    modesto
    Posts
    7
    Rep Power
    0

    Re: Fujitsu Problem

    This sounds like it might be a good solution. How did you conceal the sensor and wire? I have no attic to run wire thru. Any suggestions?