    Change walking cooler from R-12 to 409



    Can anyone tellme if the txv well work if i change system over from 12 to 409.



  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Change walking cooler from R-12 to 409

    Yes, It should work OK
    R12 and R409 TEV is the same. Why are you changing. Have you had a gas leak or a compressor burn out.
    Of its a burnout the it would be worth checking the orrice. But apart from that its the usual.
    Change drier(s) vac out and regas, check youre pressures before you fully charge if doing so by weight as quite often you will need to charge at 10% less with the new blend

    Regards

    Raymond