    rivering sight glass



    I recently started up a walkin freezer box. Receiver at 50%. temp in box is fine. How come the sight glass does not clear? 2 ton condensing unit 404a refrigerant suction @ 13 psi discharge at 200 psi no head master.Unit on top of box in a 70 ambient no restictions . This seems to fool a lot of techs They always want to clear the glass without torching the receiver ending up with an over charge.



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: rivering sight glass

    I think it's something to do with the way it is piped. Liquid line oversized? or just the fact that the pipe is going straight down to the txv.

    Just a thought.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    Join Date
    Jan 2007
    Location
    USA
    Age
    59
    Posts
    145
    Rep Power
    18

    Re: rivering sight glass

    possibly. The company I work for has a large engineering department and they can't give me a good answer. Oh well. We also design and build racks for many of the large supermarket chains.
    Cheers

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: rivering sight glass

    Quote Originally Posted by joe magee View Post
    I recently started up a walkin freezer box. Receiver at 50%. temp in box is fine. How come the sight glass does not clear? 2 ton condensing unit 404a refrigerant suction @ 13 psi discharge at 200 psi no head master.Unit on top of box in a 70 ambient no restictions . This seems to fool a lot of techs They always want to clear the glass without torching the receiver ending up with an over charge.
    flashing in the sightglass indicates a lack of subcooling, this maybe from and undercharge OR it is a restrictive liquid line causing a drop in pressure, flashing off the liquid partially to gas.

    Alternatively the sightglass maybe too close to the expansion valve, showing the every opening of the valve

    The techs should charge to a known weight or the subcooling off the condenser

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  5. #5
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: rivering sight glass

    I have had this sympton when a insufficiently sized receiver was fitted to a system the tubulance of the refrigerant entering the rceiver was causing bubbles in the outlet of the receiver showing in the sight glass. Fitted a larger receiver and the problem went away, took a bit of sorting out though.

    Ian

  6. #6
    Join Date
    Jan 2007
    Location
    Canada
    Posts
    13
    Rep Power
    0

    Re: rivering sight glass

    I remember reading too that with the 400 series refrigerants that the sight glass may not clear, due to the different components seperating and therefore a little vapor pressure shows up in the sight glass, therefore the danger of overcharging trying to clear the sight glass.