    bitzer screw compressor



    I have a hussmann rack that has open drive bitzer screw compressors. Somtimes the compressors go off on the motor starters. I reset and check my amp draw is fine . Two days later I am out again. Some have drives others dont. I am thinking a possibly voltage drop? maybe I need to put a recorder on them. voltage checks out ok 480.



  2. #2
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: bitzer screw compressor

    Hi joe magee

    If the units are within name plate perameters when you are testing them i.e during start up and running it may be wise to record over 48 hrs what exactly is happening are the loads increasing at specific times of the day or after defrost, unloading and loading etc.

    This may give you an idea for a full diagnosis.

    Regards
    Lrac

  3. #3
    Join Date
    Dec 2006
    Location
    England
    Age
    69
    Posts
    35
    Rep Power
    0

    Re: bitzer screw compressor

    How old are the starters? The conacts could be burnt & pitted, on start up the current will be off the scale of your clip-on for a moment, during this time the voltage & current can be out of balence across the phases, with bad contacts the starting conditions can be different each time.

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: bitzer screw compressor

    Quote Originally Posted by joe magee View Post
    I have a hussmann rack that has open drive bitzer screw compressors. Somtimes the compressors go off on the motor starters. I reset and check my amp draw is fine . Two days later I am out again. Some have drives others dont. I am thinking a possibly voltage drop? maybe I need to put a recorder on them. voltage checks out ok 480.
    Hi Joe
    check the oil solinoides, if they pass on off cycle this will happen. Also the oil solinoide should only be energised when your compressor goes to delta

    hope this helps

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  5. #5
    Join Date
    Jan 2007
    Location
    USA
    Age
    59
    Posts
    145
    Rep Power
    18

    Re: bitzer screw compressor

    Hi Andy. Why do the compressors trip if oil soleniod sticks open? possibly heavy load on start up? It's 480 across the line. Thanks I'll check that

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: bitzer screw compressor

    Quote Originally Posted by joe magee View Post
    Hi Andy. Why do the compressors trip if oil soleniod sticks open? possibly heavy load on start up? It's 480 across the line. Thanks I'll check that

    Hi Joe
    take a look at the bitzer web site.
    www.bitzer.de
    and download the application manual. One of the first things Bitzer say to look out for
    It's a compressor not a pump, if you get oil in there the only way to clear it is by turning the compressor over by hand, it is quite difficult and you can feel how the excessive load would feel like on a motor.

    Another possibilty would be liquid refrigerant coming back from the cases, this would trip them, but you would have multiple other faults also