    Rotor BLocked-Carrier Alarm



    First of all i'd like to say Happy New Year to all of you, thou it's too late. We have internet connection problems because of Taiwan earthquake.

    I have a problem with Carrier 30HXC Series, Screw compressor Air and Water Cooled Liquid Chiller.

    Can someone tell me, what's the meaning of ROTOR BLOCKED? Reffering to the manual, this is caused by LOAD TO HIGH.

    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Rotor BLocked-Carrier Alarm

    Sounds like the refrigerant load on the compressor is too high.

    Perhaps you need to check the expansion valve operation to ensure that the loading of the machine is correct.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2006
    Location
    Batam, Indonesia
    Age
    47
    Posts
    23
    Rep Power
    0

    Re: Rotor BLocked-Carrier Alarm

    Thx, Brian_UK,

    i have checked the running current :
    only 122 A from Design Running Ampere 263 A-156 A. Why is this so?

    The owner said that the compressor oil never been replacing for almost 3 years. Maybe this also gives some effect.

    please help

  4. #4
    Join Date
    Jan 2007
    Location
    Somewhere in England
    Posts
    13
    Rep Power
    0

    Re: Rotor BLocked-Carrier Alarm

    When does the fault occur? right after startup, at startup or a while after it has been running?

    Is the compressor getting too hot or making any unusual noises?

    If the oil is knackered it may be losing some of its lubrication properties and causing interference problems inside the compressor itself.

    Get it changed.

  5. #5
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    19

    Re: Rotor BLocked-Carrier Alarm

    I have had this a couple of times,check for arcing on contacts of compressor contactors.If they are Siemens 3RT1054,the top comes off for inspection.Sometimes the compressors pull too much current on start if contacts are badly arced.You can obtain new set of contacts without replacing whole contactor.

  6. #6
    Join Date
    May 2006
    Location
    Batam, Indonesia
    Age
    47
    Posts
    23
    Rep Power
    0

    Re: Rotor BLocked-Carrier Alarm

    This problem occur a while after it has been running.

    Now we are preparing to change the compressor's oil.