    rack oil press faillure



    have a rack , roof top location. this 4 compressor lo temp rack has locked out twice on oil fail (all compressors).any input on where the oil is hanging up to cause all units to have to be reset.



  2. #2
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: rack oil press faillure

    There are many things which could cause this..

    Post more details on the set up i.e oil separator type,refrigerant ,oil type,operating pressures / temperatures,oil managment,etc.

    It could be anything from oil seperation to flooded starts

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: rack oil press faillure

    Clean the oil seporator and any oil filters in between.

    Make sure oil in sep is at a higher pressure than the compressor bodies.

    When you return to site after they have tripped, is there oil in the compressors? How much?

    Is there oil in the sep? How much?

    Have you gone to site to check the oil levels before they get a chance to trip? What are the levels like?

    As Mark says, there is many many things that can cause oil shortage.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: rack oil press faillure

    I,ve seen a tap in the oil return line on a pack with no hole machined in it when it was made. Took some finding.

    Cheers Jon

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: rack oil press faillure

    Is this a pack already long running? (important!!)
    Height difference?
    Does the pack run longer times on partial load?
    VFD controlled?
    Lack of gass and more in general lack of gass speed is often the cause for improper oil return to the pack.
    Multiple risers?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Jul 2006
    Location
    uk
    Age
    46
    Posts
    46
    Rep Power
    0

    Re: rack oil press faillure

    are you getting liquid flood back on your pack? what type of oil switces, are they bellows type or "magic" eye type? and are they isolated when comps are not running, have known them to still be fed when comp stops and then time out. also are the overloads auto reset? that would do it too.