how to connect capacitor in three phase reciprocating compressor for chiller
i want to know how to connect capacitor in three phase reciprocating compressor.
-
18-10-2024, 10:58 PM #2
Re: how to connect capacitor in three phase reciprocating compressor for chiller
As a rule you don't need a capacitor for a 3 phase motor as the phases provide the rotating magnetic field to get the motor running.
As always though there are exceptions: https://www.refrigeration-engineer.c...-it&highlight=
To this day I'm still unclear on that Carrier motor!
Cheers,Andy.Last edited by Tayters; 18-10-2024 at 11:01 PM.
-
20-10-2024, 06:36 PM #3
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 67
- Posts
- 678
- Blog Entries
- 1
- Rep Power
- 20
Re: how to connect capacitor in three phase reciprocating compressor for chiller
Hi Easy way wiring Contactor of capacitor to run with compressor Contactor First you should calculate reactive of systems
-
27-11-2024, 04:00 PM #4
Re: how to connect capacitor in three phase reciprocating compressor for chiller
..............
Last edited by seanf; 29-11-2024 at 11:53 AM.