    Sabroe 202 LM



    Hello

    Has anyone seen an issue with a Sabroe 202 LM not being fully unloaded on shutdown?



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,378
    Rep Power
    40

    Re: Sabroe 202 LM

    No, as long as it unloads fully before start up. Has spring to unload it. What type of indication do you have for slide valve?Does it need calibration?

  3. #3
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    234
    Rep Power
    20

    Re: Sabroe 202 LM

    Yes I have seen that issue when slide valve has a quick movement, magnetic coupling of the indicator is shifted. The issue is that you reach 0% with a wrong indication but you don't reach 100% as indicated (depending of the control)
    Attached Images Attached Images

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,378
    Rep Power
    40

    Re: Sabroe 202 LM

    Cricri, Good point, have had this happen as well Can test that by removing indicator glass & turning to unload position. If you run up & does same thing, then magnetic coupling needs replacing. If LPI, then that’s another story.

  5. #5
    Join Date
    Dec 2005
    Location
    SCOTLAND
    Age
    52
    Posts
    49
    Rep Power
    0

    Re: Sabroe 202 LM

    Good Morning

    Firstly, thank you for taking the time to read and reply!

    Turns out the compressor was fully unloaded and the indicator was stuck showing a false reading of being 88% loaded.

    Thanks again cirri & RANGER1 - Have a nice day guys!