13-09-2024, 06:15 PM #1
Daikin chiller check valve
Hi everyone,
Yesterday I was checking a Daikin chiller and noticed something I had not previoulsy seen elsewhere. It is a check valve placed between the output of the receiver tank and the liquid line that goes to the EEV, while at the same time there´s a tube bypassing the receiver.
At first I thought (and maybe it actually is) a way to inject the best sub-cooled liquid you can get (directly from the condenser) but since the check valve needs a certain pressure drop to open, it looks to me that this way the receiver would actually never work.
I guess I am wrong since Daikin makes a lot of chillers, but I can not get how this works.
By the way, the chiller is heat-cool, so there´s a reversing valve as well. I tried to draw a schematic here but I am not 100% I remember correctly.
DAIKIN CHECK.jpgDAIKIN CHECK.jpg
-
13-09-2024, 06:50 PM #2
Re: Daikin chiller check valve
I suppose the diagram you provided is not quite correct.
This is a standard one for the heat pump chiller.
Refr. diagram.jpg
Cooling.jpgLast edited by narkom; 13-09-2024 at 06:53 PM.
-
16-09-2024, 11:57 AM #3
Re: Daikin chiller check valve
Thanks narkom
Yes, I guess this is the right P&ID. Not an easy one to understand either but hopefully makes more sense than what I gathered from the pictures I took.
I checked the manual but the circuit is not there. Where does this come from ?
Regards
-
17-09-2024, 08:25 PM #4
Re: Daikin chiller check valve
This is from Trane CXAH manual. Since the plate evaporator and fin&tube condenser have a different internal volume, the circuit needs a receiver to store an excess of refrigerant during the cooling mode.