    Hi everyone,

    Yesterday I was checking a Daikin chiller and noticed something I had not previoulsy seen elsewhere. It is a check valve placed between the output of the receiver tank and the liquid line that goes to the EEV, while at the same time there´s a tube bypassing the receiver.

    At first I thought (and maybe it actually is) a way to inject the best sub-cooled liquid you can get (directly from the condenser) but since the check valve needs a certain pressure drop to open, it looks to me that this way the receiver would actually never work.

    I guess I am wrong since Daikin makes a lot of chillers, but I can not get how this works.

    By the way, the chiller is heat-cool, so there´s a reversing valve as well. I tried to draw a schematic here but I am not 100% I remember correctly.

    DAIKIN CHECK.jpgDAIKIN CHECK.jpg
    Attached Images Attached Images



  2. #2
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    142
    Rep Power
    23

    Re: Daikin chiller check valve

    I suppose the diagram you provided is not quite correct.
    This is a standard one for the heat pump chiller.

    Refr. diagram.jpg

    Cooling.jpg
    Last edited by narkom; 13-09-2024 at 06:53 PM.

  3. #3
    Join Date
    Aug 2005
    Location
    ARGENTINA
    Age
    59
    Posts
    28
    Rep Power
    0

    Re: Daikin chiller check valve

    Thanks narkom

    Yes, I guess this is the right P&ID. Not an easy one to understand either but hopefully makes more sense than what I gathered from the pictures I took.

    I checked the manual but the circuit is not there. Where does this come from ?

    Regards

  4. #4
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    142
    Rep Power
    23

    Re: Daikin chiller check valve

    This is from Trane CXAH manual. Since the plate evaporator and fin&tube condenser have a different internal volume, the circuit needs a receiver to store an excess of refrigerant during the cooling mode.