    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    May 2006
    Yorkshire
    73
    419
    Daikin floor mounted split -
    Why does Daikin recommend a minimum 3m pipe run and what are consequences if it's say a 2m run?
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
    ireland
    54
    1,459
    41
    Re: Daikin floor mounted split -
    The system is charged for up to 25m so at 2m there is a risk of liquid coming back, you could recover charge and recharge with 2m worth.
    Apr 2008
    Southampton, England
    49
    1,027
    36
    I've seen larger splits (10kW size) make a drumming noise through the pipes, I think it's the pulsating of the compressor. A longer run sorted the problem so I guess it was something like the extra length help absorb the pulses. On smaller splits I've not seen it as a problem (saw one where the wall mount tails were piped directly to the outdoor).
    LG had some units years back where you had to take some refrigerant out if the run was a certain length.
    Cheers,
    Andy.
    nevgee's Avatar
    May 2006
    Yorkshire
    73
    419
    Thanks for the info.
