    As customers are requesting higher evap temps I am trying to determine the BTUH of our MT display cases at those requested temps. i.e 20f, 22f, 24f etc. I have a Coriolus flow meter and all the software working well and have baseline information at a 20f evap. To simulate different rack temps I've installed a simple Sporlan ORIT, EPR valve. Raising the EPR presure from 20 to 22, psi converted, the Superheat changes and we have a cat and mouse game to get the system balanced again and SH always winds up high even when TXV is wide open.
    My question; What am I missing.
    Feb 2011
    scotland
    469
    Re: Setting EPR and TXV
    What type of expansion valve are you using?
    How does the rest of the system look? Subcooling, liquid line sight glass, filters and strainers clean?
    Dec 2005
    228
    Using a sporlan SBVE-AA TXV. which has worked for us for many years @20f evap temp. The condensing unit is one we pair with this case set-up all the time with TXV factory preset SH .
    Full charge, all components are new so filters and strainers are clean.
    Feb 2011
    scotland
    469
    Quote Originally Posted by kengineering View Post
    Is the sizing of the EPR ok?
    Do you have a sight glass you can use to check you have a constant solid liquid supply to the TXV?
    3,365
    Are you calculating superheat on the evaporator pressure, upstream of EPR valve?
    Dec 2005
    228
    SH calculated at the access port at the TXV sensing bulb.
    3,365
    https://www.parker.com/content/dam/P...-090/90-20.pdf
    Do you have any flow through EPR when TX valve fully open & what is pressure upstream & downstream at that point.
    Instruction suggest 30 minutes settling period.
    Air on/off temperatures also gives good information on how it is working or not.
    You could treak pressure setting down a little to see if flow etc comes back as a test.
    ireland
    54
    1,453
    Fitting an EPR will mess with TXV as you are putting a false restriction on the suction line, the EPR will open / close to maintain its setting irrespective of the TXV. I only come across EPR on rack type systems to allow higher suction pressures on display cases.
    Dec 2005
    228
    Thanks for all the idea sharing. Seems we just needed to make very small adjustments and be patient. One of the difficulties I face is working from home and trusting that my guidence to the Lab Guys is understood and executed.
    Thanks again, Ken