    Cycle Stops at Low Suction Pressure



    We have split a/c unit, the brand is Carrier-a water cooled condenser, water from the water chiller scroll type of compressor. Just 1 month ago, I experienced low suction. I made leak testing from the evaporator to condenser but no leak found. I tried to vacuum the unit inorder to check if it is leaking nothing goes wrong. Everytime I charged refrigerant the pressure goes to 2.5 bar then slowly goes to 2 bar, then tripped. When I fully charge, the compressor stops it takes me time to bleed. I already changed liquid filter nothng happened. I adjust the flow of water from the condensing pressure of 14 Bar to 11 Bar, it seems it take long to tripped but still the pressure is reducing. I suspect that the evaporator pressure regulator or the compressor something doing this problem.

    Can anyone share your ideas.



  2. #2
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    191
    Rep Power
    19

    Wink Re: Cycle Stops at Low Suction Pressure

    TEV?Or NRV leaks.

    Renato

  3. #3
    kuuleun's Avatar
    kuuleun Guest

    Re: Cycle Stops at Low Suction Pressure

    Hello everyone, I am just joint w/ this forum.
    If unit use Thermostatic Exp. , the bulb sensor could be damage, I suggest to change TEV

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Cycle Stops at Low Suction Pressure

    Hello Kuuleun and welcome to the forum.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Nov 2005
    Location
    Moscow
    Posts
    20
    Rep Power
    0

    Re: Cycle Stops at Low Suction Pressure

    ...water cooled condenser

    Pay attention to temperature of water it maybe too cold

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    24
    Rep Power
    0

    Re: Cycle Stops at Low Suction Pressure

    What is the model number of the Chiller? The Electronic expansion device that is more than likely fitted on your machine is 1800 step. You can check the windings of the internal EXV motor by removing the cable and measuring the resistance across each of the five pins. You should measure aroung 32 ohms.

  7. #7
    Join Date
    Oct 2007
    Location
    Zacatelco Tlaxcala
    Age
    54
    Posts
    5
    Rep Power
    0

    Re: Cycle Stops at Low Suction Pressure

    If you have a solenoid valve may be this not opens totally