    compressor heater... always on with compressor ?



    hi guys

    I have a small'ish 3 phase compressor at work running a small room, it's setup to be a freezer, but its normally run as a fridge (just changing the temp on the thermostat)

    just realised the other day that the compressor heater coil is powered up whenever the compressor is running... is this right ?

    seam's like a hell of a waste cooling the motor windings with the gas return, then heating the oil (I'm guessing its the oil?) with an electric heating coil.... who not use the hot gas output ?

    I'm guessing it shouldent be powered up all the time ? compressors run hot enough on there own !



  2. #2
    Join Date
    May 2005
    Location
    Minnesota
    Age
    52
    Posts
    19
    Rep Power
    0

    Re: compressor heater... always on with compressor ?

    typically a crankcase heater is operating during the off cycle

  3. #3
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18

    Re: compressor heater... always on with compressor ?

    I use crankcase heater in large system to prevent migration of refrigerant to the compressor.
    Since we have in our country a high ambient temperature, i don't even bother to install one in small systems.

    For your purpose, i think you should only have it ON when the compressor is OFF. thus, saving some dime for your valued customer.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: compressor heater... always on with compressor ?

    If the compressor is shutting off in pump down, then you even don't need one at all.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jul 2006
    Location
    New Berlin, Wisconsin, USA
    Age
    65
    Posts
    57
    Rep Power
    18

    Re: compressor heater... always on with compressor ?

    Normally they are off while running. Having it on when the compressor is running can increase the potential for breaking down the oil, if you have a higher than normal superheat. The heater serves to not only reduce the amount of refrigerant that may migrate back, but it also serves to warm the oil so everything gets oil at startup.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: compressor heater... always on with compressor ?

    If the evaporator(s) are pumped down prior to the compressor shutting off, the crankcase heater is only needed if the crankcase temperature falls below the saturation temperature of the suction pressure.

    In cold ambient conditions (around the compressor) the heat loss out of the crankcase can allow the oil to become diluted with refrigerant. This is what the heater is trying to prevent by keeping the oil warm.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: compressor heater... always on with compressor ?

    To prevent the heater burning, interlock the heater with the compressor contactor normally closed contact, so that only on stop the heater is on, and viceversa.

  8. #8
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: compressor heater... always on with compressor ?

    Hi I would suspect the contactor has been changed at some time an rewired incorrectly.Check to see if the heater is wired through the normally closed contacts so when the contactor is energised the supply is taken off the heater.


    Regards Bernard

  9. #9
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    Re: compressor heater... always on with compressor ?

    it's wired right into the came contactor as the compressor... the wires for the compressor and heater are littrally joined

    looks like another one for me to re-wire !

    pity I didn't look at this sooner, would have saved me a fortune !

    the compressor always pumps down when it turns off.... I wired this in myself in the main control box... the heater and compressor contactor is ontop of the room so I didn't see it

  10. #10
    jimbo 10's Avatar
    jimbo 10 Guest

    Re: compressor heater... always on with compressor ?

    agree with bernard make sue the heater supply is on an normally open contact on contactor or aux heater should be of when comp running

  11. #11
    jimbo 10's Avatar
    jimbo 10 Guest

    Re: compressor heater... always on with compressor ?

    sorry normally closed