Results 1 to 25 of 25
Thread: RDM Products
    Sep 2006
    here uk
    42
    5
    Question RDM Products
    Does anyone else use the RDM range of products? Case controllers and front end systems? They are currently the systems of choice for M&S and Somerfield i believe.
    If so what are your opinions about them? Do you find them user friendly?
    What common problems do you encounter with them?
    rbartlett's Avatar
    rbartlett Guest
    Re: RDM Products
    Done a v.small amount on a few M&S -thought they were pretty good and quite reliable. However the compressor mounted ones are prone to vibrational problems..I believe I have some manuals around.
    However there are far better informed guy's here for sure ;-)
    Richard
    Jun 2001
    N.Ireland
    1,630
    Re: RDM Products
    Quote Originally Posted by BenService View Post
    Hmmm RDM,
    sorry to say I don't like them. A bit plastic in appearance, really Elm in a new box. With the EEV's they use probes for the evaporation not a transducer, a cheap way to get an evaporator referance, but not as good or relyable as a transducer.
    A cheap alternative to Danfoss, easier to set up and with a front end that is more user friendly than Danfoss.
    They come in power trays that, you just pull out the plugs and plug in the new one, just set the dip switches and defrosts and away you go.
    Better than TEV's but not as good as Danfoss.
    Still they do not do the same job technically as Danfoss or save as much energy, a cheap mans Danfoss.
    We have been fitting them, but only on certain stores, not our top end brands
    Kind Regards Andy
    PS all the manuals are freely available from their site on the net.
    Mar 2004
    624
    21
    Re: RDM Products
    Our M&S,s have recently changed from elm to R.D.M.I think they have the best call centre by far,The front end is very user friendly.
    I,ve had problems with vibration on the packs and found changing the scroll compressor rubber mounts from soft to hard and fit the correct spacers cures the problems.
    The biggest problem is the cases,I can,t remember the manufacture,they have PT 1000 probes which are the best on the market but for some strange reason they decided to put 4 connections between the probe and the controller.
    I,ve not had much to do the the new case controllers and don,t normally look into these things in advance,I think you learn better a 3 am under a bit of pressure.
    Regards Bernard
    Mar 2004
    624
    21
    Re: RDM Products
    Quote Originally Posted by Andy View Post
    Hmmm RDM,
    Kind Regards Andy
    Hi Andy
    I,m interested in what youv,e said ref eev,s and tev,s the reason being 99% of the supermarkets I look after are on eev,s and have a lot of problems with a large ice build up at the back of the evap on freezers.The cases with tev,s hardly require de-icing.The eev,s evap probes fail quite regular.As well as the armatures jamming open on the screw pack freezers.I find flood back is also more common on eev cases.Maybe its the quality and accuracy of the probes.I always thought if they fitted tev,s they would have less problems.I,ve never seen tranducers used on cases only on packs.
    Kind Regards Bernard
    Jun 2001
    N.Ireland
    1,630
    Re: RDM Products
    Quote Originally Posted by bernard View Post
    Hi Andy
    Hi Bernard
    At a guess the evaporator probes are wrongly located. If you fit a set of gauges on the shrider connection on the case, the probe should read exactly that, if it doesn't then the controller needs to be offsett or the probe moved (the probe must be in the coldest point on the coil).
    By fitting transducers this problem doesnot occur, hence the danfoss system does not freeze up like that.
    I have seen one case where a large cold store cooler has broken all the fan blades, the Danfoss EEV's kept running, away down at 3 and 5 %, the cooler did not freeze up and no liquid carry over occured.
    If you mention EEV's people think they are all the same, the probe type will work, but the probe must be located at the coldest point and probably offset after this. You can sometimes do all this and still find the refrerance temperature wanders, purely by the fact that 400 series refrigerant has a glide and you simply don't know what part of the mixture is evaporating at the probe, this will vary with evaporator loading.
    Transducers are the way to go, we usually fit one per case controller, one or two section, but one transducer will do a row of cabinets, if fitted to the main header and you will notice little differance to a transducer per case.
    If you are fitting RDM, they will tell you use the Danfoss probes, they have a better life cycle.
    Hope this helps,
    Kind Regards Andy
    Oct 2004
    Scotland
    1,454
    21
    Re: RDM Products
    LOL.. are we talking about the same people?
    I have only ever phoned them twice and on both times I felt I had woken the guy up out of a deep sleep. And even then he wasn't much help.
    Chillin
    and go get a cuppa
    Oct 2004
    Scotland
    1,454
    21
    Re: RDM Products
    And thats another thing.. what happens when the front end fails..?
    RDM say you have to send it back to them!!!!!!
    How can a supermarket go through a day let alone a week without an alarm panel????
    We had RDM go round and update the front ends and he f^&cked them all up. Another guy had to go round and fix them all.
    Chillin
    and go get a cuppa
    Mar 2004
    624
    21
    Re: RDM Products
    Quote Originally Posted by chillin out View Post
    Chillin
    They answered the phone didn,t they,thats a good call centre in my book. .It was a chap from wales that did our new systems,he obviously practised on your ones first. Trying working with parasence they go home at 5pm and switch the phones off
    Regards Bernard
    Jul 2003
    Ireland
    10
    Re: RDM Products
    Hmmm RDM,
    Tend to agree with you there.
    But my real objection to RDM is that they sell direct to end users, so while they want me to promote their product now, when it's established (say with a chain) I'll be cut out. No thanks.
    Mar 2004
    624
    21
    Re: RDM Products
    Yes tranducers is the way ahead,However I,ve not seen them fitted on any supermarket cases.Rdm are fitting PT1000 probes which are bullet proof.RMS will also be using these probes with there new controllers.
    I not surprised they resemble elm as its the same software engineers that designed it.Elm now comes under trend who are both owned by honeywell.I find both trend and elm have a couldn,t care less attitude when speaking to them.However I do like elm products.
    Regards Bernard
    Sep 2006
    here uk
    42
    5
    Thumbs down Re: RDM Products
    I myself deal with RDM on a daily basis and have experienced a lot of the problems others have mentioned. If you ring the technical help 90% of the time you'll get through to Norman or Dal or Cal cant remember his name, Normans ok but the other bloke can be a bit obtuse and make you feel like it's your fault for the break down.
    No support after 5ish, i've left over five stores for longer than 48 hours with no alarm cover for their fridges, because A: you cant get hold of anyone after 5 and so that means another visit the next day to confirm that the rdm data manager has failed (very common problem), and B: because you have to wait for rdm to issue you a returns number, and if they dont think that its the equipment gone wrong due to technical failure you then have to order the equipment at your own cost and return the old one to get a refund.
    Mar 2004
    624
    21
    Re: RDM Products
    This does not sound good at all,we can only comment on the experiences we,ve had.I will be very peed off it this happens to me.
    Regard Bernard
    Mar 2006
    kent
    49
    22
    Re: RDM Products
    just today 15/9 i had to ring their tech desk due a pack controller in a somerfield petrol station.it`s only been open 9 months and already had 2 pack controllers and i had to order another today because the last one locked up.same old sh#te.i agree though,it did sound like i woke the bloke up and it was only 9 am.
    Mar 2006
    kent
    49
    22
    Re: RDM Products
    i do hope no-one from rdm is looking at this.if you are can i please have my controller before christmas?
    Jun 2001
    N.Ireland
    1,630
    Re: RDM Products
    Hi Guys
    why even bother with all this hassle, fit danfoss I keep an AKC 114 and 115 in the van, an EKC 414 and a gateway. The only time I take them out off the van is if we are short one on an install
    About a year ago I did replace one AKC115 that failed after 6 years, and two dead on arrival 114,s.
    Three controllers in one year and I am the only one that carries an AKC 115 in the van, with none in the stores.
    Me I don't work on plant if it hasn't Danfoss fitted I get by quite nicely without the hassle.
    Kind Regards Andy
    Sep 2006
    here uk
    42
    5
    Re: RDM Products
    Danfoss kit is quite nice, i've had limited use of it but seems to be reliable, i'd say every tesco store i've been on use it. Going back to the rdm pack controllers, a site i visited was using them in a 2 searle packs, the hp transducer had failed and had been on backup for a while, but then the backup transducer failed, so another firm who attended the call nicked the spare backup transducer off the other pack, low and behold both packs are running on back up. replacement parts where ordered by the other company, apparently 3 weeks wait?? anyway, the rdm controllers can be configured for other types of trancducers or so the documentation says, so i get into the setup menu go to the appropriate parameters enter the tranducer offset, range and something else, do you think it would run? no chance, even in the documentation they quote incorrect figures for the danfoss tranducer they use. if you've got all day, empty fridges on the shop floor and dont mind the frequent no remote monitoring due to system failure, RDM's products are for you!
    Andy Riddell's Avatar
    Andy Riddell Guest
    Re: RDM Products
    There is no denying that danfoss controllers are a good controller but talk about a useless shortform and hidden settings,for instance on the 414 if you don't set up the start defrost after power drop every controller will go on defrost at the one time.They also have no built in timer so you can have them as stand alone but the defrost set up is a bit basic.I commissioned the first 414 sites in scotland and trying to get info on them was a nightmare they also can only go IP and not RS485.So in general every manufacturer has it's good and bad,I've found that most complaints are actually due to engineers lack of knowledge and incompetence.
  19. #19
    Oct 2004
    Scotland
    1,454
    21
    Re: RDM Products
    I like Danfoss as well, but I don't understand why they put some parameters in them that you would never ever need to set that way.
    Also, when they fail, they seem to set themselves to the most daftest settings.
    Chillin
    and go get a cuppa
  20. #20
    Jan 2007
    scotland
    159
    Re: RDM Products
    if you think rdm are poor wait until you have problems with the carel case controllers that sainsburys are using,one shop under two years old has had loads of controller fails,yet the thousands of danfoss controllers in tescos run with never any problems
  21. #21
    scotland
    756
    Re: RDM Products
    its amazing to read all the different engineers veiws on controllers i agree that danfoss is very reliable however they are not very user friendly at all and you need a degree in quantum physics to even adjust a parameter never mind commission a whole store however getting back to the issue raised rdm make the best pound for pound controller on the market and iff your working on the m and s contract just phone oaksmere and they will dial in and do any adjustments for you
  22. #22
    Jan 2008
    8
    Re: RDM Products
    Dear Fowlie
    Please I would really appreciate whether you can tell me the sort of problems you have been experiencing with Carel controls.
    Obviously any comments will help us to take any action if necessary.
    Meantime should you require any further information, please do not hesitate to contact us at careluk@careluk.co.uk
    Looking forward to hearing from you
    Carel UK Aftersales
    Quote Originally Posted by fowlie View Post
  23. #23
    Jan 2008
    49
    82
    Re: RDM Products
    talking of carel controllers, has anyone got a set of parameters for an ir33 controller as used in sainsburys rather than the 92 page tome on the website in several languages. would be appriciated!
    jon
  24. #24
    Jan 2008
    8
    carel uk
    Please provide your full email address a PDF file be enlcosed.
    Carel Uk after sales
    Quote Originally Posted by chillled View Post
    jon
  25. #25
    Split Croatia
    57
    6,151
    36
    Re: carel uk
    Quote Originally Posted by careluk View Post
    Hi, Carel UK!
    I am glad that someone from great company as Carel is with us.
    In short time, I will post some questions for you!