Thread: not cold enough
    Jan 2005
    48
    64
    Smile not cold enough
    hi all
    I had a look at a Leibherr fridge freezer today.
    Freezer fine but fridge not getting down to temp. Fridge compressor seems to run but evap panel starts to freeze, measured these values(celcius) after about 5 minutes of compressor starting.....
    discharge 39
    Liquid 32
    suction 23
    The liquid temp rises quite fast, compared to the discharge temp.
    If the super cool button is pressed then it gets down to temp as it runs continuously for 6 hours but ices up and goes warmer when this has finished.
    model KGTves5066-24, on R600
    Any ideas?
    I dont normally work on domestics so i'm not familiar and i've never worked with R600, should I be worried about working with it?
    Jan 2003
    East Anglia
    1,160
    Re: not cold enough
    Dont worry about R600, its a gas same as R134
    There are slightly different precautions to take when going into the system but as a gas its same as ever.
    You didnt say anything about the stat.
    Normal problem with fridge/freezers is that they use one stat on the freezer section so the frisge is not controlled on temp. Obviously there is a plate evap in the fridge to cool it down when the freezer is running but as soon as it gets to -20 off it goes.
    Now being a new unit i would like to think the insulation is good so if the freezer door is left closed and its fairly full of stock holding it at temp the compressor may not come on for an hour or so.
    Obviously in that time the fridge door may be open an indefinnate amount of times.
    Is it just a single stat ?, Ive just realised i may have typed all that for no reason.
    Fatboy
    Jun 2005
    Romania
    213
    Re: not cold enough
    u should check the pressures, at this aspect it lucks to be overcharged, are us shore u did charge the right amount of refrigerent, what did happend with the fridge that it needed intervention, and what are the pressures
    Jan 2005
    48
    64
    Re: not cold enough
    Thanks guys,
    The fridge has its own lcd control, seperate from the freezer,its own probe at the top of the fridge behind a glass panel and its own compressor.
    Its a fairly new model with no obvious modifications from the factory so no schraeder points to check pressures.
    Mar 2006
    belfast
    239
    Re: not cold enough
    Is The The Unit In A Warm Place R600 Cant Cope With Heat, Try Switchin It Off Over Nite And Try Again It Should Be Ok, Usaly Just Change To 134a Myself
    Jan 2005
    48
    64
    Re: not cold enough
    Its just in a normal household kitchen, why is the suction temp so high?
    Oct 2006
    1,843
    21
    Re: not cold enough
    You state temps and not pressures. Did you fit your gauges or just measure the temp. From the info you give it looks to me as though the comp is not pumping. Possible valve problem and discharge pressure is seeping back causeing high suction pressure and therfore high suction temp.
    Ceers taz.
  1. Cold Room Design - minus 25deg C
    By vijay_study in forum Fundamentals
    Last Post: 11-11-2009, 07:12 AM
  2. cold river water
    By eftimios in forum Fundamentals
    Last Post: 09-11-2008, 06:37 PM
  3. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Last Post: 26-07-2006, 10:52 PM
  4. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Last Post: 12-03-2006, 09:20 PM
  5. Freezer not cold enough, Fridge too cold
    By barrance in forum Commercial
    Last Post: 06-12-2001, 06:11 PM