Results 1 to 11 of 11
    9
    Russell defrost heater wiring help
    Is it possible to use 240volt heaters wired in series with 480 volt supply voltage?
    Jan 2006
    Re: Russell defrost heater wiring help
    As long as the heaters are similar, have the same wattage, yes.
    9
    Thank you for the help
    9
    Russell said it cant be done, but I think it can. Any one have any reason why I shoudnt try it, or does anyone have any other info on this subject that could reassure me?
    11,024
    I think Walden is wrong, you could use the 240vac heaters connected to a 240vac supply split off your 480vac supply and that would be OK.
    Feb 2005
    Jamaica
    121
    Just a thought Rob ,on a 480 system one leg and earth would give u what? 277 I think, are u going to connect your 240 heater to one leg and earth? If so wont u be 30 volts over? or there abouts and your 240 heater is it live and neutral or is it 2 115v lines
    Just thinking out aloud ,any takers
    9
    Yes from ground each leg will be 277vac I am guessing that two heaters wired in series single phased out between two legs would work
    11,024
    Wired in series will still give you a 240v item connected to a 277v supply !
    Feb 2001
    Tampa Florida
    1,076
    Hmmmm. If I had a 1,000 ohm heater and wired it up to 230 Volts, I would draw .23 amps and have a wattage of 52.9. If I wired 2 1,000 ohm heaters in series and wired them up to 460 Volts, I would have .23 amps and 105.8 watts. But if I wired the 2 heaters in parallel to 230 volts my amperage would double but my watts would be the same. I would think it is okay. Perhaps I am missing something regarding Ohm's law?
    9
    If 2 wired in series 2x240 would be 480?
    Oct 2001
    Nottingham UK
    5,667
    Quote Originally Posted by Rob@goldcoast
    Before we can determine the answer we need the wattage of the heaters
    Using Ohms Law (W = V x A) and transposing (A = W / V)
    Assuming each heater to be 1000W in series (2000W total and applying 240 volts to neutral we would get
    (2000 / 240) = 8.33A FLC
    Applying 480V to neutral you would get
    (2000 / 480) = 4.16A FLC
    If you are talking of 480V 2 phase then this is something different
  1. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Last Post: 25-09-2009, 06:24 PM
  2. Single pole contactor & crankcase heater
    By herefishy in forum Air Conditioning
    Last Post: 01-04-2009, 08:38 AM
  3. Homemade Heat pump water heater
    By busman in forum Technical Discussions
    Last Post: 05-02-2008, 04:04 PM
  4. Hot Gas defrost suction pressure regulation
    By 87mustang in forum Technical Speculations
    Last Post: 05-08-2005, 07:25 AM
  5. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Last Post: 08-03-2005, 07:50 PM