Results 1 to 11 of 11
  1. #1
    Join Date
    Aug 2006
    Location
    USA
    Posts
    9
    Rep Power
    0

    Russell defrost heater wiring help



    Is it possible to use 240volt heaters wired in series with 480 volt supply voltage?



  2. #2
    Join Date
    Jan 2006
    Location
    UK
    Posts
    53
    Rep Power
    19

    Re: Russell defrost heater wiring help

    As long as the heaters are similar, have the same wattage, yes.

  3. #3
    Join Date
    Aug 2006
    Location
    USA
    Posts
    9
    Rep Power
    0

    Re: Russell defrost heater wiring help

    Thank you for the help

  4. #4
    Join Date
    Aug 2006
    Location
    USA
    Posts
    9
    Rep Power
    0

    Re: Russell defrost heater wiring help

    Russell said it cant be done, but I think it can. Any one have any reason why I shoudnt try it, or does anyone have any other info on this subject that could reassure me?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Russell defrost heater wiring help

    I think Walden is wrong, you could use the 240vac heaters connected to a 240vac supply split off your 480vac supply and that would be OK.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Feb 2005
    Location
    Jamaica
    Posts
    121
    Rep Power
    20

    Re: Russell defrost heater wiring help

    Just a thought Rob ,on a 480 system one leg and earth would give u what? 277 I think, are u going to connect your 240 heater to one leg and earth? If so wont u be 30 volts over? or there abouts and your 240 heater is it live and neutral or is it 2 115v lines
    Just thinking out aloud ,any takers

  7. #7
    Join Date
    Aug 2006
    Location
    USA
    Posts
    9
    Rep Power
    0

    Re: Russell defrost heater wiring help

    Yes from ground each leg will be 277vac I am guessing that two heaters wired in series single phased out between two legs would work

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Russell defrost heater wiring help

    Wired in series will still give you a 240v item connected to a 277v supply !
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Russell defrost heater wiring help

    Hmmmm. If I had a 1,000 ohm heater and wired it up to 230 Volts, I would draw .23 amps and have a wattage of 52.9. If I wired 2 1,000 ohm heaters in series and wired them up to 460 Volts, I would have .23 amps and 105.8 watts. But if I wired the 2 heaters in parallel to 230 volts my amperage would double but my watts would be the same. I would think it is okay. Perhaps I am missing something regarding Ohm's law?

  10. #10
    Join Date
    Aug 2006
    Location
    USA
    Posts
    9
    Rep Power
    0

    Re: Russell defrost heater wiring help

    If 2 wired in series 2x240 would be 480?

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Russell defrost heater wiring help

    Quote Originally Posted by Rob@goldcoast
    Is it possible to use 240volt heaters wired in series with 480 volt supply voltage?
    Before we can determine the answer we need the wattage of the heaters

    Using Ohms Law (W = V x A) and transposing (A = W / V)

    Assuming each heater to be 1000W in series (2000W total and applying 240 volts to neutral we would get
    (2000 / 240) = 8.33A FLC

    Applying 480V to neutral you would get
    (2000 / 480) = 4.16A FLC

    If you are talking of 480V 2 phase then this is something different
    Last edited by frank; 19-08-2006 at 12:16 AM.

Similar Threads

  1. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Replies: 19
    Last Post: 25-09-2009, 06:24 PM
  2. Single pole contactor & crankcase heater
    By herefishy in forum Air Conditioning
    Replies: 7
    Last Post: 01-04-2009, 08:38 AM
  3. Homemade Heat pump water heater
    By busman in forum Technical Discussions
    Replies: 20
    Last Post: 05-02-2008, 04:04 PM
  4. Hot Gas defrost suction pressure regulation
    By 87mustang in forum Technical Speculations
    Replies: 5
    Last Post: 05-08-2005, 07:25 AM
  5. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Replies: 26
    Last Post: 08-03-2005, 07:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •