    Eqivelant Pipe Length



    I was looking through the latest manufacturers catalogue the other day and noticed that the maximum pipework length between indoor/outdoor unit had increased from 50m for an R22 unit to 70m for an R407c unit.
    Can anyone explain why this is?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Higher pressures, different compressors ?

    No, now that I think more deeply, I do not know why...sorry.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Smile

    Can you give us some more info? Which manufacturer / unit?

    Then we may be able to repond

  4. #4
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    The manufacturer put more lubricant in the crankcase????maybe?

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    sorry for the lack of information but it was Daikin a/c equipment, which we install quite a lot of, and, when doing a site survey, I was always thinking along the line of maximum indoor / outdoor limits, but suddenly I read the latest info sheets and was staggered to learn that the maximum length was increased to 70m for 407c.

    No explanation has been forthcoming from Daikin and I can't really work out why this should be without technical backup.

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, i don't do much split work, but I was at the wholesalers one day and the Tech/sales guy was showing a new range he was selling. After looking through the leaflet I spotted the increaed pipe lengths before you have to add refrigerant, I asked why and he said simply that's what people want. The customer (us) have asked for something and they have responded.
    He may have been spoofing, but it sounded good.
    Regards. Andy.

  7. #7
    Join Date
    Dec 2001
    Location
    Canada
    Age
    70
    Posts
    52
    Rep Power
    23
    If you follow good piping practices you can just ignore what the manufacturers say about maximum lengths... Do your homework on the pipe sizing and consider the refrigerant and oil charges and you can cool Britain from Canada!

  8. #8
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23
    Hi Gibson
    Sorry i'm so late with this question BUT how can you say that it dos'nt matter about pipe length, when a compressor is only able to pump it's rated amount of refrigerant .

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    In a stabilized, closed loop, series system, the mass refrigerant flow is identical at all points.

    In other words, if the compressor is pumping X pounds of refrigerant per minute, then the rate of flow at every point in the system is X pounds per minute.

    The problem with cooling Britain from Canada would be friction. Friction anywhere slows the flow everywhere, resulting in the compressor reducing it's flow to match.

    On the other hand, angled fittings are of much more concern than straight pipe length, each providing the friction equivalent of many feet of straight pipe. This is the equivalent length of the fittings.

    Increasing the equivalent length by 20 meters isn't going to add a lot of friction. The effect on the system will be minimal, and can be compensated for by slightly reducing the friction at the choke point, i.e. metering device. In a TEV system, this would happen automatically.

    As regards the rest of Gibson's post, I agree wholeheartedly.
    Last edited by Gary; 24-03-2002 at 08:35 PM.

  10. #10
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23
    If that's true Gary why do manufacturers give a maximum pipe length

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    If that's true Gary why do manufacturers give a maximum pipe length
    Because they are selling a one size fits all product, containing refrigerant and oil charges, metering device, pipe sizes, etc. which must perform reasonably at both minimum and maximum pipe lengths. Compensatory changes can be made, but they aren't counting on your ability to make those changes.

    A few meters of pipe length can be added to their maximum by simply redefining "perform reasonably", and/or maybe adding a few ounces of this or that.

    There are a lot worse things that can happen to a system than a little extra friction. You might find it difficult to measure a difference in performance caused by 20 meters of extra piping, although you may need to add a little refrigerant to fill the extra liquid line.

  12. #12
    Join Date
    Dec 2001
    Location
    nottingham
    Age
    62
    Posts
    96
    Rep Power
    23
    OK Gary i see your point
    but does that mean that even with a pipe run that is longer than the manufacturers maximum they will still honour the warrenty on the equipment.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I suspect so, and I don't see why not, but you would have to ask them to know for sure. Personally, I wouldn't tell them. What are they going to do...come out and measure?

  14. #14
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Wink Re: Eqivelant Pipe Length

    Bored at work and trawling through old threads found this one and thought i would bring it up to date! Had a problem with a split type system i wont mention any brands. Unit installed was new model with new pipe limits *problems* *problems* Lets just say i didnt work so the message here is always stick within the Equivelant or actual piping limits to cover yourself and yes they will come out and measure the pipe work
    Last edited by puddleboy3; 23-03-2006 at 10:33 AM.

  15. #15
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Eqivelant Pipe Length

    As a manufacturer of big DX close control with generously sized liquid receivers, I can only recommended a maximum of 15 meters of equivalent pipe length. Beyond that, a pipe layout design is required with appropriate refrigerant piping accessories.
    Too long discharge pipe will result in unexpectedly high HP, while a too long liquid pipe will not do too much harm, but starvation.
    The point is that oil must be added, and god knows how much, not too little or not too much, and excessive liquid migration in the condenser coil in winter time at standstill, which will result in condenser drowning and low pressure alarms while standby (in countries of harsh winters and all year long operation, like computing centres).
    So beware of generous manufacturers. No one gives away anything for free.

  16. #16
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Thumbs up Re: Eqivelant Pipe Length

    Try to calculate pressure drop.Danfoss have good program for calculation.If pressure drop cose ading 3 C to condesation or 3 C to suction temperature should be ok.

    Best regards,
    Renato

  17. #17
    Join Date
    Jan 2006
    Location
    Fort Worth, Texas
    Age
    74
    Posts
    19
    Rep Power
    0

    Re: Eqivelant Pipe Length

    Hello, I am working on a similar problem, as well. I need to calculate the amount of R-22 required to recharge several systems where someone walked-off with the line sets overnight at a supermarket. #1 system- a produce cooler (24 ft.) has a 125' line length, lineset - 1/2" liquid and 1 1/8" suction with a Heatcraft condenser (HD10502M6C) and an antique Tyler case (Y12TVBH 1041B) Mfg. pressure setings Cut in: 36 and Cut out: 14-19. I must calculate the amount of refrig. required for the bid price, and I'm not sure how to go about it. Can anybody give me a clue where to start?

  18. #18
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Eqivelant Pipe Length

    Measure the total lineal feet of each pipe. Then find the volume of each pipe. (lineal feet times pipe cross sectional area in square feet = cubic feet)

    For the suction line charge multiply the suction line volume (cubic feet) times the vapor density at the suction pressure.

    Cubic feet of volume times pounds per cubic foot. That will give the total refrigerant charge for the suction line. Similar process for the other piping.

    For the liquid line charge multiply the liquid line volume (cubic feet) times the liquid density at condensing the pressure.

    For the discharge line charge multiply the discharge line volume (cubic feet) times the vapor density at the condensing pressure.

    You will need to add some charge for the receiver, since the diptube in the receiver must have a liquid seal on it before liquid can flow out.

    Heatcraft should have the condenser charge in a catalog somewhere. If you are using head pressure controls to flood the condenser, you also need to find out how much this will be.

    In Texas this is probably not too bad. If the system were installed in Montana, it would be a different story.

    Add all of the different amounts of refrigerant and you have your total. To be safe add 20% to this amount so you have enough money allowed for minor changes.

  19. #19
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Eqivelant Pipe Length

    NoNnickName, visted last Thursday X-Change (Flumignano) and Intherm (Gregorio di Veronella, nearby Verona)
    They will start a production with oval pipes in their drycoolers.
    Both factories were very clean, well organised and I was impressed of what I saw at X-Change.
    Are you also a customer of Intherm?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  20. #20
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Eqivelant Pipe Length

    No, I'm not, but will take a look

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Eqivelant Pipe Length

    Daniele Stolfo is the present boss, previous founder or co-founder of Thermokey.
    The oval tube is in my opinion a nice 'invention'
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Eqivelant Pipe Length

    Quote Originally Posted by frank
    I was looking through the latest manufacturers catalogue the other day and noticed that the maximum pipework length between indoor/outdoor unit had increased from 50m for an R22 unit to 70m for an R407c unit.
    Can anyone explain why this is?
    The molecular weight of R-22 and 407c are nearly the same , However say at 40*F SST the cuft/lb of 407c is less then that for R-22 therefor less pressure drop so a longer suction line is possible.
    Last edited by wambat; 27-03-2006 at 02:13 AM.

Similar Threads

  1. Single room a/c - long pipe run?
    By electro in forum Air Conditioning
    Replies: 7
    Last Post: 07-08-2006, 09:49 PM
  2. pipe sizeing tool
    By Latte in forum Tools and Calculators
    Replies: 5
    Last Post: 10-12-2003, 11:32 PM
  3. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  4. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •