    Compressor sizing using R404a



    Hi all,

    I would like to seek advise on sizing the reciprocating compressor (Carlyle brand). Base on the Heat Load Calculation, the sensible and latent heat gain is about 100kW. Using the psychrometric chart, my required cooling capacity is about 300kW.

    I have problem trying to determine refrigerant data such as, the Saturated suction temperature, liquid temperature before and after condenser etc temp related data.

    I assume I would need these data to determine the mass flow of refrigerant and in order to determine the size of the compressor.

    I have tried using the Carwin software for compressor sizing, however the software required the temperature data to size the compressor too.

    Please advise. Many thanks.



  2. #2
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    191
    Rep Power
    19

    Exclamation Re: Compressor sizing using R404a

    My advice is get a book.

    Renato

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Compressor sizing using R404a

    Quote Originally Posted by PCL
    Hi all,

    I would like to seek advise on sizing the reciprocating compressor (Carlyle brand). Base on the Heat Load Calculation, the sensible and latent heat gain is about 100kW. Using the psychrometric chart, my required cooling capacity is about 300kW.

    I have problem trying to determine refrigerant data such as, the Saturated suction temperature, liquid temperature before and after condenser etc temp related data.

    I assume I would need these data to determine the mass flow of refrigerant and in order to determine the size of the compressor.

    I have tried using the Carwin software for compressor sizing, however the software required the temperature data to size the compressor too.

    Please advise. Many thanks.
    Hi PCL

    I will try and help you, but your knowledge is a bit basic in some areas

    OK start at the start. What room temperature (dry bulb) do you want. For example 22 deg c with an evaportor Temperature Difference of (TD) of 6K AND a line loss of 2K due to pressure drop, then you Saturated suction would be 14 deg c. Now look at your latent heat load, if you want remove moisture from the air (you will normally need to for comfort). Saturation point or where you start to remove moisture is probably about 13 deg c (you will need your evaporation lower than this to remove moisture), possibly 8 deg c evaporation at the evaporator (this you will be able to determine on the psychrometric chart) that add a 2 deg link loss, giving you a compressor saturated suction of 6 deg c.

    Now select you condensing tempearture 10k above ambient air say the air was 35 deg, add 1k line loss and your condensing temperature would be 46 deg c.

    Subcooling,depends on you fridge design, but 3 k would get you started.

    Let me know if this makes sense.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Compressor sizing using R404a

    Andy has provided some information there.

    I also think you have another issue that should be more important right now.

    Quote Originally Posted by PCL
    Base on the Heat Load Calculation, the sensible and latent heat gain is about 100kW. Using the psychrometric chart, my required cooling capacity is about 300kW.
    Your load calculation has a difference of 300%. That needs to be resolved before you worry about selecting compressors, etc.

  5. #5
    Join Date
    Jul 2005
    Location
    Northern Ireland
    Age
    47
    Posts
    8
    Rep Power
    0

    Re: Compressor sizing using R404a

    Good Advice andy

Similar Threads

  1. R507 instead R404a?
    By Friobernal in forum Refrigerants
    Replies: 49
    Last Post: 09-04-2011, 12:42 AM
  2. capillary sizing for R404a
    By ding in forum Technical Speculations
    Replies: 8
    Last Post: 19-03-2008, 08:27 PM
  3. hitachi utopia g7 r404a not up to cooling
    By peter1927 in forum Trouble Shooting
    Replies: 12
    Last Post: 16-01-2006, 04:19 AM
  4. piping selection for R404A
    By drk_in in forum Tools and Calculators
    Replies: 5
    Last Post: 14-11-2005, 07:33 AM
  5. R404a Oil Return
    By dallan in forum Industrial
    Replies: 1
    Last Post: 23-08-2004, 12:40 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •